Ring final circuit, 2.5mm T+E, 32 amp over current protection.
433.1.204 says 2.5mm minimum cable size.
Is that for the ring, and unfused spurs?
For example, a small load device needs to be fed by a single socket outlet, fed in 1.5mm T+E, from an unfused spur off the ring (in fact a single socket outlet next to a double socket outlet on the RFC). Fault current complies, it has RCD protection, and the plug top fuse gives the overload protection, but 433.1.204 says it must be 2.5mm cable to the single socket.
Is that correct?