Equipotential bonding and voltage

I have some questions about protective equipotential bonding.

main protective bonding .
I understand the principle, that with no potential difference no current will flow

I'm wondering about volt drop.
You will get volt drop if you have a flow of current.

So if you have two extraneous CPs and you are in between them.
One has 230V on it, and the bonding raises the potential of the other, Ext CP to 230V so no difference

Now if an insulating section was put in between one of the Ext parts  as in the example 600Ω

I am wondering what would be the outcome.

This is a standing voltage, and current would not flow between the equal potentials ?
(If there was no other path.)

But would it flow between the 230v and 70v example.
Would you actually get this volt drop?



Picture might say it better.

Parents
  • Well, in the situation as drawn, it is not clear why the upper section would  be at 70V, if the lower is 230V, We must assume that not shown is a touch over a couple of hundred ohms to external ground to get that 170V dropped over the 600 ohms (the 200R and 600R dividing the 230V between them in the ratios 200/800 and 600/800 )

    If there is no path to ground, then it all floats at about 230V wrt terra-firma, as there is no current flowing, and no voltage difference to drive that current. An equipotential zone, to use the definition.

    However, assuming there  is such a path, off sheet somewhere, then as you show, the chap downstairs gets no shock but the one upstairs does. Adding a sup bond where you show it means neither of them get a shock, but maybe now someone outside does instead, depending on where that path to ground is.

    Mike.

Reply
  • Well, in the situation as drawn, it is not clear why the upper section would  be at 70V, if the lower is 230V, We must assume that not shown is a touch over a couple of hundred ohms to external ground to get that 170V dropped over the 600 ohms (the 200R and 600R dividing the 230V between them in the ratios 200/800 and 600/800 )

    If there is no path to ground, then it all floats at about 230V wrt terra-firma, as there is no current flowing, and no voltage difference to drive that current. An equipotential zone, to use the definition.

    However, assuming there  is such a path, off sheet somewhere, then as you show, the chap downstairs gets no shock but the one upstairs does. Adding a sup bond where you show it means neither of them get a shock, but maybe now someone outside does instead, depending on where that path to ground is.

    Mike.