Equipotential bonding and voltage

I have some questions about protective equipotential bonding.

main protective bonding .
I understand the principle, that with no potential difference no current will flow

I'm wondering about volt drop.
You will get volt drop if you have a flow of current.

So if you have two extraneous CPs and you are in between them.
One has 230V on it, and the bonding raises the potential of the other, Ext CP to 230V so no difference

Now if an insulating section was put in between one of the Ext parts  as in the example 600Ω

I am wondering what would be the outcome.

This is a standing voltage, and current would not flow between the equal potentials ?
(If there was no other path.)

But would it flow between the 230v and 70v example.
Would you actually get this volt drop?



Picture might say it better.

Parents
  • (v) any metal pipework and other extraneous metal entering the location (not IN the location) is connected back to ME.

    It's seems the regs are satisfied if extraneous CPs have an insulating section on entry to a building, or are effectively connected to the MET on entry to the building.

    Which make its sound like as long as I confirm that, my duty is done.
    But I wonder about these EXT CP as they travel through the building. 

    On a periodic inspection. I R2 wonder lead pipe work in bathrooms. This is where I get into doubt.
    I know the pipe work satisfies the regs on entry into the building, but does not in a location.

    Because everything is generally hidden and tiled over, we only have out meter readings to go on.
    So I get a 600Ω reading on pipework back to the MET or a high sup bond reading in the location.

    What to do?? Not worry and let the RCD take care.

    But  we not satisfying note 6  701.415.2 as we are no longer effectively connected to the MET?

Reply
  • (v) any metal pipework and other extraneous metal entering the location (not IN the location) is connected back to ME.

    It's seems the regs are satisfied if extraneous CPs have an insulating section on entry to a building, or are effectively connected to the MET on entry to the building.

    Which make its sound like as long as I confirm that, my duty is done.
    But I wonder about these EXT CP as they travel through the building. 

    On a periodic inspection. I R2 wonder lead pipe work in bathrooms. This is where I get into doubt.
    I know the pipe work satisfies the regs on entry into the building, but does not in a location.

    Because everything is generally hidden and tiled over, we only have out meter readings to go on.
    So I get a 600Ω reading on pipework back to the MET or a high sup bond reading in the location.

    What to do?? Not worry and let the RCD take care.

    But  we not satisfying note 6  701.415.2 as we are no longer effectively connected to the MET?