From a containment perspective, what is the minimum separation distance between LV power (230V-400V) and unscreened UTP cable in the UK?
From a containment perspective, what is the minimum separation distance between LV power (230V-400V) and unscreened UTP cable in the UK?
From a containment perspective, what is the minimum separation distance between LV power (230V-400V) and unscreened UTP cable in the UK?
For copper data cabling indoors, the minimum separation for safety is 50 mm, but in some circumstances, 150 mm is required (see Clause 5.4.4.2 of BS 6701). The requirement applies even if one or both cables are in metallic containment, and/or separated by metallic screen, and apply regardless of whether BS 7671 requirements for zero separation of different voltage bands.
There are also separation requirements for EMC, in BS EN 50174-2 for indoor cables (required by Clause 5.4.4.1 of BS 6701). This aligns with the guidance in Section 444 of BS 7671 (see A444.4).
Outdoors, an outdoor grade cable is to be used, and again an assessment of EMC, surge protection (if required) as well as insulation for different voltage bands. The requirements are in BS EN 50174-3. You might need to consider Table A444.2 of BS 7671 outdoors, depending on what power cables you are close to.
For both indoor and outdoor cases, the worst-case minimum should be used when safety and EMC are taken into account - for example, if safety says 50 mm and EMC says zero segregation, then use 50 mm - or of EMC says 150 mm and safety 50 mm, use 150 mm.
Some guidance on the above, and the wording of the relevant Clauses in BS 6701, can be found in:
From a containment perspective, what is the minimum separation distance between LV power (230V-400V) and unscreened UTP cable in the UK?
For copper data cabling indoors, the minimum separation for safety is 50 mm, but in some circumstances, 150 mm is required (see Clause 5.4.4.2 of BS 6701). The requirement applies even if one or both cables are in metallic containment, and/or separated by metallic screen, and apply regardless of whether BS 7671 requirements for zero separation of different voltage bands.
There are also separation requirements for EMC, in BS EN 50174-2 for indoor cables (required by Clause 5.4.4.1 of BS 6701). This aligns with the guidance in Section 444 of BS 7671 (see A444.4).
Outdoors, an outdoor grade cable is to be used, and again an assessment of EMC, surge protection (if required) as well as insulation for different voltage bands. The requirements are in BS EN 50174-3. You might need to consider Table A444.2 of BS 7671 outdoors, depending on what power cables you are close to.
For both indoor and outdoor cases, the worst-case minimum should be used when safety and EMC are taken into account - for example, if safety says 50 mm and EMC says zero segregation, then use 50 mm - or of EMC says 150 mm and safety 50 mm, use 150 mm.
Some guidance on the above, and the wording of the relevant Clauses in BS 6701, can be found in: