Minimum separation distance between LV power (230V-400V) and unscreened UTP

From a containment perspective, what is the minimum separation distance between LV power (230V-400V) and unscreened UTP cable in the UK? 

 

Parents
  • Data cabling that is susceptible to interference. 

  • Data cabling that is susceptible to interference. 

    Potentially, all copper data cabling is susceptible to interference, more so unscreened (as UTP). Having said that twisted pair (where the pairs are used as a pair, as in RS 422, RS485 and Ethernet) is less susceptible then untwisted, unscreened, data cable, for example as used for older serial links/RS232 etc. RS423 is a bit of a mix of both, being differential receive and common-mode transmit, so needs care to get the maximum lengths of run.

    Provided you meet the safety requirements, follow the guidance in A444.4 for segregation in BS 7671, either the BS EN 50174-2/BS EN 50174-3 approach, or Table A444.2 if the conditions for Table A444.1 are not met.

    You can also consider earthed metallic containment (conduit or trunking).

    If you let us know the specific application of the UTP, and what are the power cables are doing, and their voltages and currents, we may be able to be more specific.

  • Hi,

    Regarding the above query. I have a hospital design project, and have a question regarding Band 1 and Band 2 and the segregation required. I have screened network fibre cable, and LV power being FP500 which is SWA feeding FAP, and FP200 enhanced looping the fire detection devices etc. Will is be acceptable to install all cabling systems on 2 compartment basket, meaning I will install the Fibre and FP200, for the device loops on one side and the LV power on the other side of the compartment. FP500 cable is rated to 300V/500V, and the FAP require 230V supply. 

Reply
  • Hi,

    Regarding the above query. I have a hospital design project, and have a question regarding Band 1 and Band 2 and the segregation required. I have screened network fibre cable, and LV power being FP500 which is SWA feeding FAP, and FP200 enhanced looping the fire detection devices etc. Will is be acceptable to install all cabling systems on 2 compartment basket, meaning I will install the Fibre and FP200, for the device loops on one side and the LV power on the other side of the compartment. FP500 cable is rated to 300V/500V, and the FAP require 230V supply. 

Children
  • I have screened network fibre cable, and LV power being FP500 which is SWA feeding FAP, and FP200 enhanced looping the fire detection devices etc.

    These are questions for BS 5839-1, not just BS 7671, and also perhaps the relevant devolved national HTMs.The following are specifically relevant:

    • If the fibre cable is not associated with the fire alarm system critical path, then it should be in separate containment - see 26.2 k) of BS 5839-1:2017.
    • With respect to LV and loop cables of the FAS, sharing the same containment, see 26.2 l) and n) of BS 5839-1:2017, and this will depend on the FAS manufacturer's EMC advice as well as the choice of cables.