The IET is carrying out some important updates between 17-30 April and all of our websites will be view only. For more information, read this Announcement

fire alarm containment colour

I was wondering if there is any regulation saying to use only RED conduit, trunking, boxes etc for fire alarm wiring ?

It relates to the installation of alarm system in prefabricated switchgear enclosures to be precise.

We normally use galvanised containment but this time our customer would like to have PVC containment instead.

Is white containment will be also fine in this case?

Parents
  • BS 5839-1:2017, 26.2 Recommendation:

    o) All fire alarm cables should be of a single, common colour that is not used for cables of general electrical services in the building, to enable these cables to be distinguished from those of other circuits.
    NOTE 15 The colour red is preferred.

    However, I'm not sure that it is applicable in your case.

Reply
  • BS 5839-1:2017, 26.2 Recommendation:

    o) All fire alarm cables should be of a single, common colour that is not used for cables of general electrical services in the building, to enable these cables to be distinguished from those of other circuits.
    NOTE 15 The colour red is preferred.

    However, I'm not sure that it is applicable in your case.

Children