Ungrounded Neutral on 115 Vrms, 400 Hz Power Supply Secondary

On one of our facilities we have come across a 400 Hz, 115 Vrms power supply whose secondary side neutral does not appear to be connected to facility earth and is effectively floating.  Approx. 50 Vrms Neutral to GND is observed on the secondary side of the power supply unit. 

Some observations are:

  1. The power supply units are installed "fixed" within the electrical installation and wired in permanently (not portable).
  2. The PSU is class I equipment as is the downstream equipment connected to it
  3. The PSU chassis is connected to PE on the incoming supply
  4. The PSU output includes a thermal magnetic circuit breaker, implying the OEM intends for ADS to be used as the chosen method of protection against electric shock
  5. We can't see any OEM facility inside the power supply for the Neutral and PE to be connected on the secondary side
  6. There doesn't appear to be a route for a "Line" to "Exposed Conductive Part" fault currents to make their way back to the secondary side of the PSU neutral and so the thermal magnetic breaker and ADS is questionable
  7. There is no insulation monitoring installed on the secondary side
  8. We have gone back to the OEM to ask how their system design meets the intent of the wiring regulations for protection against electric shock but we are not getting an answer

Does anyone have any thoughts on why the OEM might have taken this approach or any specific regulation requirements we need to be cognisant of before proceeding further?  My initial thoughts are that we need to introduce another neutral to PE reference link on the output side of the PSU for the purpose of ADS and also to prevent issues with floating neutral voltages downstream.

Thanks,

Richard

Parents
  • ADS has been assumed ... but does the system and connected equipment use something else ... double or reinforced insulation, for example?

  • Agreed - or even separated - either for one item (see BS 7671 section 413)  or several (section 418.3).

    Is whatever is connected to the secondary side of the PSUs fixed? If it's just a socket outlet that anything could be plugged into, the secondary side might not come under BS 7671 anyway (like a lot of smaller UPSs) but come under some equipment standard that may have its own ideas about shock protection (the basic principles are likely to be similar to BS 7671's but sometimes the significant details can vary). I've a feeling that 400Hz is slightly safer than 50/60Hz from a shock perspective too - which again might influence some details.

       - Andy.

  • or even separated - either for one item (see BS 7671 section 413)  or several (section 418.3).

    Possibly ... I was also thinking that we don't know what these supplies do, and therefore whether they are part of the electrical installation (under BS 7671) or machinery as defined in the Supply of Machinery (Safety) Regulations (under BS EN 60204-1) ... but that doesn't really affect the classification.

  • Hello,

    Thank you for your replies.

    ADS has been assumed ... but does the system and connected equipment use something else ... double or reinforced insulation, for example?

    ADS is assumed because the 400 Hz power supply feeds multiple items of class I equipment and the exposed conductive parts of these items are not isolated from the exposed conductive parts of other circuits and also have fortuitous connections back to facility PE via the local metalwork which is connected to the MET.

    Is whatever is connected to the secondary side of the PSUs fixed?

    The PSU output circuit breaker feeds fixed 400Hz distribution boards (fixed installation) and these have individual fuses for the final circuits.  Final circuits then feed out to break out "patching panels" (fixed installation) on our facility and these connect to current using equipment on the units under test (UUT).  The UUT are not fixed and get swapped out for each test and our technician teams rig and patch the equipment using mil spec connectors and the like.

    I was also thinking that we don't know what these supplies do, and therefore whether they are part of the electrical installation

    As above - these feed aircraft OEM parts on the UUT.  However, in order to make the connections to the UUT our operators are in proximity to the earthed metalwork of the test rig, as well as the fortuitously earthed exposed conductive parts of the UUT (fed by the ungrounded 400 Hz, 115Vrms PSU).

    Agreed - or even separated - either for one item (see BS 7671 section 413)  or several (section 418.3).

    I would struggle to agree that we have met the requirements for either section.

    If you take the view that this information is necessary to safely maintain the equipment, and check it continues to be safe, the perhaps Section 6 of the H&S@W etc Act 1974 requires it to be provided. Check out 6(1A)(c).

    Agreed - we will make the appropriate enquiries and seek to make rectifications as soon as possible.

    Given the above, I am concluding that we should be implementing ADS to mitigate the risk of electric shock presently.

    Many thanks,

    Richard 

Reply
  • Hello,

    Thank you for your replies.

    ADS has been assumed ... but does the system and connected equipment use something else ... double or reinforced insulation, for example?

    ADS is assumed because the 400 Hz power supply feeds multiple items of class I equipment and the exposed conductive parts of these items are not isolated from the exposed conductive parts of other circuits and also have fortuitous connections back to facility PE via the local metalwork which is connected to the MET.

    Is whatever is connected to the secondary side of the PSUs fixed?

    The PSU output circuit breaker feeds fixed 400Hz distribution boards (fixed installation) and these have individual fuses for the final circuits.  Final circuits then feed out to break out "patching panels" (fixed installation) on our facility and these connect to current using equipment on the units under test (UUT).  The UUT are not fixed and get swapped out for each test and our technician teams rig and patch the equipment using mil spec connectors and the like.

    I was also thinking that we don't know what these supplies do, and therefore whether they are part of the electrical installation

    As above - these feed aircraft OEM parts on the UUT.  However, in order to make the connections to the UUT our operators are in proximity to the earthed metalwork of the test rig, as well as the fortuitously earthed exposed conductive parts of the UUT (fed by the ungrounded 400 Hz, 115Vrms PSU).

    Agreed - or even separated - either for one item (see BS 7671 section 413)  or several (section 418.3).

    I would struggle to agree that we have met the requirements for either section.

    If you take the view that this information is necessary to safely maintain the equipment, and check it continues to be safe, the perhaps Section 6 of the H&S@W etc Act 1974 requires it to be provided. Check out 6(1A)(c).

    Agreed - we will make the appropriate enquiries and seek to make rectifications as soon as possible.

    Given the above, I am concluding that we should be implementing ADS to mitigate the risk of electric shock presently.

    Many thanks,

    Richard 