Would this be a C3 rather than C2

In a light industrial environment (dry food packaging factory) we use an external company to carry our EICR inspections on substations and associated sub distribution and fixed wiring every three years. 
The EICR has identified that there is no evidence of 6 monthly RCD/RCBO functional tests (there are labels stating last RCD instrument test about 2 years ago) and marked this down as a C2, surely this would only be a C3? 
Industrial EICR frequency is recommended between 3-5 years dependent on environment, risk assessment etc. I would accept a C2 if there was no evidence of testing within last 5 years, but surely is a C3 within this period?

Parents
  • It is not at all clear what the potential danger to life is - if an RCD was actually faulty and failed to trip on the day when the test button was pressed, then that's a C3 or a C2, depending on what role the RCD is providing.

    Note  it is not a C1 unless when the button is pressed the cover falls off and exposes live metal to the touch .

    Not being clear what the RCD protects due to absent labels maybe warrants a C3 as well, and a recommendation to re-label things I suppose 

     However, just "not able to find previous test results" is the normal condition on very many sites I suspect - On that basis the inspector must go around awarding C2s to everyone they visit.

    As described it sounds to be something of a bit of a jobsworth matter

    ( i,e someone over enthusiastically (mis)using their modicum of authority in a way to make their role become more important than it really is, usually to the inconvenience and irritation of others)

    .

    Mike.

  • I agree, definitely no C1, failing to trip on button or >300mS with instrument test at 1xI∆n I would give a C2, but absence of evidence of biannual function test (common in domestic environments) or instrument test within 5 years (max recommended industrial EICR period) or missing labels is surely only a C3 at most.

    Definition of C2 :-

    C2 - Potentially dangerous - urgent remedial action required.
    This means that this fault is not immediately dangerous in the same way as a C1 code is, but it could quickly become a hazard in the future.

    Even if due to production constraints, they couldn’t test the RCD/RCBO, that does not indicate that it is potentially dangerous and need urgent remedial action.

    It would surely have to be a C3 at most?

Reply
  • I agree, definitely no C1, failing to trip on button or >300mS with instrument test at 1xI∆n I would give a C2, but absence of evidence of biannual function test (common in domestic environments) or instrument test within 5 years (max recommended industrial EICR period) or missing labels is surely only a C3 at most.

    Definition of C2 :-

    C2 - Potentially dangerous - urgent remedial action required.
    This means that this fault is not immediately dangerous in the same way as a C1 code is, but it could quickly become a hazard in the future.

    Even if due to production constraints, they couldn’t test the RCD/RCBO, that does not indicate that it is potentially dangerous and need urgent remedial action.

    It would surely have to be a C3 at most?