EICR Coding of PV & EESS Poor Practice

Evening all,

First time I've posted in a long time, first time on this new set up.

Did an EICR today that took in a small outbuilding with an old FIT PV system installed.  Since this installation another company has added a second inverter and a battery.

The outbuilding is supplied with a 2.5 SWA to a garage style distribution board with a 40A 30mA RCD main switch (AC type), personally think the sub main to this building should have been upgraded prior to the initial solar being installed.

The new inverter and battery is fed directly from the original system rotary isolator (via another isolator).  This is all supplied via a B16 MCB.  The PV inverter is rated at 4kW and the battery inverter is 3kW.

My thoughts are that obviously each inverter should be on it's own circuit, there is also the issue of the new inverter and battery now being connected to the FIT export meter.  But for me the big one is if the battery is full and the PV is in optimum conditions you could have a overload situation. There is the B16 MCB to potentially limit this and there apparently haven't been any incidences of nuisance tripping.

C2 or C3, what does everyone think?

Chriso 

Parents
  • My thoughts are that obviously each inverter should be on it's own circuit, there is also the issue of the new inverter and battery now being connected to the FIT export meter.  But for me the big one is if the battery is full and the PV is in optimum conditions you could have a overload situation.

    The latest guidance on this is available in the 3rd Ed of the IET CoP for EESS.

    According to BS 7671:2018+A2:2022, there is the current rating of CUs to consider, as well as circuits ... although the issues were also covered in a similar manner for 2nd Ed of the IET CoP (big change is the consideration of the calculation of minimum CSA, S).

Reply
  • My thoughts are that obviously each inverter should be on it's own circuit, there is also the issue of the new inverter and battery now being connected to the FIT export meter.  But for me the big one is if the battery is full and the PV is in optimum conditions you could have a overload situation.

    The latest guidance on this is available in the 3rd Ed of the IET CoP for EESS.

    According to BS 7671:2018+A2:2022, there is the current rating of CUs to consider, as well as circuits ... although the issues were also covered in a similar manner for 2nd Ed of the IET CoP (big change is the consideration of the calculation of minimum CSA, S).