Hi
I have a fairly rudimentary question regarding earth fault loop impedance by calculation to determine maximum disconnection time requirements per BS7671.
Some calculations I have come across simply calculate Zs from the combined resistance of the cables within the installation, it strikes me that this omits the impedance associated with the source (e.g., a supply transformer) and load (e.g., an AC motor) devices, where the latter should have some influence in the case of a fault to earth in the motor windings.
This warrants further consideration in the case of >100A applications, where the guidance of GN6 also incorporates reactance in the fault current equation.
Are source/load (i.e., devices and not cables) impedances commonly accounted for in earth fault loop impedance calculations? And if so how (e.g., the case for a 415V transformer feeding an AC motor)?
Or would measurements on the as-built installation always be preferable when applying such considerations? With reactance coming into play via LCR measurement.
Many thanks in advance.