I had a large electricity supplier install solar PV and battery system and the import meter melted followed by the export meter.

They are stating that it is my issue and not there's as I have overloaded my consumer unit.

The import meter was rated to 100A

The export meter was rated to 100A

My incomer is protected by an 80A fuse

My export meter is on a supply protected by a 50A MCB

They are saying it is not their issue and I will have to go through the Ombudsman if I don't agree with their report.

How do I deal with a large company that refuses to take responsibility for faulty workmanship.

   

Parents
  • In the bit of photo we can see, it looks rather like the dreaded loose neutral screw effect  again - the live wires at the top out of shot I presume are in tip top condition ? 

    Are they implying by their statements about your consumer unit,  that their design is not adequately protected against a perfectly credible overload condition ?

    I suggest collecting pictures of all the bits, as well as what wire sizes have been used.

    I assume its one of these https://www.metermarket.co.uk/product/eastron-sdm230-mbus-mid-single-phase-direct-connected-100a-energy-meter.

    15KW is a lot, but a 100 fuse and 230V suggests max steady load of 23kW, plus transient excursions above that - was the installation  not foreseeing a likely level of load ?

    M

  • Thanks, I had a gas boiler and no EV at the time of installation

  • My incoming fuse is rated at 80A and I have no issues, but these meters are rated at 100A and one is on a circuit protected by a 50A breaker. I am having trouble with the maths saying it was overloading issues if I haven't been over 80A?

  • indeed and I'm not too clear what section is protected by what,

    -but as described  I'm struggling to see

    a) how they think you have overloaded it

    b) if that really is what they think, why they designed you a system that could not handle the likely current.

    And more likely if the neutral is burnt but not the live, that is a classic 'one loose screw' issue - both sides should look equally cooked as they carry identical current.

    M.

Reply
  • indeed and I'm not too clear what section is protected by what,

    -but as described  I'm struggling to see

    a) how they think you have overloaded it

    b) if that really is what they think, why they designed you a system that could not handle the likely current.

    And more likely if the neutral is burnt but not the live, that is a classic 'one loose screw' issue - both sides should look equally cooked as they carry identical current.

    M.