I've just been having a discussion about the outer sheath colour of soft skinned (FP 200 TYPE ) from the mains distribution board to the fire alarm isolator. I always thought it should be white and not red - any thoughts ??
I've just been having a discussion about the outer sheath colour of soft skinned (FP 200 TYPE ) from the mains distribution board to the fire alarm isolator. I always thought it should be white and not red - any thoughts ??
BS5839 recommends red, although it is not mandatory;
regards, burn
Many thanks, I've been looking for information regarding BS 7671 as well they are bound to have a different view I suppose
Many thanks, I've been looking for information regarding BS 7671 as well they are bound to have a different view I suppose
I've been looking for information regarding BS 7671 as well they are bound to have a different view I suppose
BS 7671 has no requirements for the colour of the sheath of a multicore cable. In respect of fire alarm systems, BS 7671 references BS 5839 series, BUT I'm aware that there are references back to BS 7671 for some aspects of BS 5839 ...