Please I would like to know what percentage of cross section area should my neutral cable be with respect to the live conductor for a total harmonic distortion limit of less then 5% at nominal frequency of 50Hz
Please I would like to know what percentage of cross section area should my neutral cable be with respect to the live conductor for a total harmonic distortion limit of less then 5% at nominal frequency of 50Hz
Sounds like something for section 5.5 of appendix 4 of BS 7671. You probably need a few more details (like how well loads are balanced across phases) to get a complete answer, but as I read it an ordinary full size N (i.e. 100% of L) will cope with up to 15% distortion.
- Andy.
Sounds like something for section 5.5 of appendix 4 of BS 7671. You probably need a few more details (like how well loads are balanced across phases) to get a complete answer, but as I read it an ordinary full size N (i.e. 100% of L) will cope with up to 15% distortion.
- Andy.