Please I would like to know what percentage of cross section area should my neutral cable be with respect to the live conductor for a total harmonic distortion limit of less then 5% at nominal frequency of 50Hz
Please I would like to know what percentage of cross section area should my neutral cable be with respect to the live conductor for a total harmonic distortion limit of less then 5% at nominal frequency of 50Hz
Sorry I was trying to say A 3 - phase 4-wire system
is there such a thing as a 400V single phase load?
is there such a thing as a 400V single phase load?
I understand some welders are (connect between two lines of a 3-phase plug, as they require more power than 230V single phase can comfortably deliver, but can't easily make use of 3-phase) also some stadium or sports field lighting (where the large distances make 230V a problem with voltage drop).
- Andy.
one example: https://www.elclampsonline.com/shop/flood-lighting/mhn-fc-2000w740-400v-xw/
- Andy.
is there such a thing as a 400V single phase load?
You can't rule it out ... they used to be more common than they are now, and mainly industrial or heating/lighting loads in commercial applications.
one example: https://www.elclampsonline.com/shop/flood-lighting/mhn-fc-2000w740-400v-xw/
- Andy.
That would, of course, need a suitable ballast ... but agreed
We're about to take you to the IET registration website. Don't worry though, you'll be sent straight back to the community after completing the registration.
Continue to the IET registration site