It and Iz

Im getting a bit confused with It and Iz, and which is out final value when calculating cable size

It  - the value of current tabulated in this appendix for the type of cable and installation method concerned, for a single circuit in the ambient temperature stated in the current-carrying capacity tables

Iz -  the current-carrying capacity of a cable for continuous service, under the particular installation conditions concerned.

In =32  Ca 0.87

so    It ≥  32 / 0.87

It ≥ 36.78A

Look up tables in BS 7671  clipped direct (c) one  2 core cable   

4mm=36A

6mm= 46A

So we go with 46A

So our It (Tabulated value we look up) is 46A and we will use a 6mm2 cable

So what is Iz?

Iz ≥ In ≥ Ib  understand the relationship

Now Iz = It x correction factors.
Iz = 46 x 0.87 =  40.02A  which is greater than In (32A) so thats OK

But we got a value of 36.78 A when applying correction factors to In

We also have this formula... 

It ≥ Iz / correction factors

40.02 / 0.87 = 46

We end up with the same number.

We have a calculated value of 36.78A  in the book the cable choice is 6mm which is rated at 46A 

I'm struggling to see what we would call our final cable choice? Its not Iz , but the description (continuous service) makes it sound like it is

What is Iz

Hope that make some sense

Its based around this IET article


electrical.theiet.org/.../appendix-4-of-bs-7671.pdf

Parents
  • Thank you both for two really helpful replies.


    I have tried to follow the process you mentioned as in the EIDG

    This is a really simple example I have chosen. probably too simple 

    We have the information we know.
    Then we have the desired  Iz

    Is this right?

  • That doesn't look quite right to me. Fundamentally we need the cable as installed to carry the required current (in this case Ib = In) so I would have thought that Iz ≥ In would do. The correction factors convert It to Iz where the installation conditions differ from what's assumed by the tables.

    I'd probably say your 26.3A is the minimum required It (rather than Iz).

    Yes, 20.67A is the Iz of the cable as installed - which meets your required CCC  of 20A.

      - Andy.

Reply
  • That doesn't look quite right to me. Fundamentally we need the cable as installed to carry the required current (in this case Ib = In) so I would have thought that Iz ≥ In would do. The correction factors convert It to Iz where the installation conditions differ from what's assumed by the tables.

    I'd probably say your 26.3A is the minimum required It (rather than Iz).

    Yes, 20.67A is the Iz of the cable as installed - which meets your required CCC  of 20A.

      - Andy.

Children
  • 2.4.3 in EiDG


  • 2.4.3 in EiDG

    Humm, I won't have the latest version to check against, but I wonder if you're spotted a typo there. To my mind it should be It ≥ In/C (or Iz  ≥ In).

       - Andy.

  • 2.4.3 in EiDG

    This ONLY applies for rewireable fuses to BS 3036. For other OCPDs to standards quoted in BS 7671, Cf = 1

    So, to use your example: In = 20 A.

    We then use the following formula to see what value we need to look up in the Tables in Appendix 4:

    (a) If this circuit is NOT protected by a 20 A rewireable fuse, but by say a 20 A circuit-breaker, then (using your example) we have Ca = 0.87, Ci = 0.88, and all the other C factors = 1, so:

    It ≥ 20 ÷ (0.87 × 0.88) = 20 ÷ 0.7656

    or  It ≥26.12 A.

    If I am using 'clipped direct' and want to select 2c+E 'flat' UK cable, I look in Table 4D5, column 8, and see the first cable that meets the requirement 'It at least 26.12 A' is 2.5 sq mm with It = 27 A.

    (b) If this is protected by a 20 A rewireable fuse, then (using your example) we have Ca = 0.87, Ci = 0.88, Cf = 0.725, and all the other C factors = 1, so:

    It ≥ 20 ÷ (0.87 × 0.88 × 0.725) = 20 ÷ 0.5551

    or It ≥36.02 A

    If I am using 'clipped direct' and want to select 2c+E 'flat' UK cable, I look in Table 4D5, column 8, and see the first cable that meets the requirement  'It at least 36.02 A' is 4.0 sq mm with It = 37 A.