It and Iz

Im getting a bit confused with It and Iz, and which is out final value when calculating cable size

It  - the value of current tabulated in this appendix for the type of cable and installation method concerned, for a single circuit in the ambient temperature stated in the current-carrying capacity tables

Iz -  the current-carrying capacity of a cable for continuous service, under the particular installation conditions concerned.

In =32  Ca 0.87

so    It ≥  32 / 0.87

It ≥ 36.78A

Look up tables in BS 7671  clipped direct (c) one  2 core cable   

4mm=36A

6mm= 46A

So we go with 46A

So our It (Tabulated value we look up) is 46A and we will use a 6mm2 cable

So what is Iz?

Iz ≥ In ≥ Ib  understand the relationship

Now Iz = It x correction factors.
Iz = 46 x 0.87 =  40.02A  which is greater than In (32A) so thats OK

But we got a value of 36.78 A when applying correction factors to In

We also have this formula... 

It ≥ Iz / correction factors

40.02 / 0.87 = 46

We end up with the same number.

We have a calculated value of 36.78A  in the book the cable choice is 6mm which is rated at 46A 

I'm struggling to see what we would call our final cable choice? Its not Iz , but the description (continuous service) makes it sound like it is

What is Iz

Hope that make some sense

Its based around this IET article


electrical.theiet.org/.../appendix-4-of-bs-7671.pdf

Parents
  • Sorry, This is the last I will post on this 
    But this is a calculation using 2.4.0  (EIDG) equation first.
    Then the equations from BS7671


    I can provide this feedback, and perhaps some appropriate publications could be devised to fill the gap, if there is one?

    I really believe there is a gap and a need. Believe me I look and I can't find many publications that go into the little details, and give a full explanation and worked examples. There is a lot of regurgitation and old content out there.
    But I may of missed some so any suggestions gratefully accepted.

    And thank again for the help

  • Hello,
    I have not been following the discussion in its entirety, but I would like to clarify whether ( Iz ) is simply the value of ( It ) after applying the correction factors. I hope this is the case, as I have been in this profession for 30 years and this has been my understanding.

  • There is no term as far as I am aware for the calculated value, just our 'It' has to be ≥ than that value.
    That has been a major part of my confusion. Though I think I have it now, thanks to the advice in this thread.
    Be nice to give it a nameSlight smile

  • I have not been following the discussion in its entirety, but I would like to clarify whether ( Iz ) is simply the value of ( It ) after applying the correction factors.

    NO.

    The two are not directly related.

    Iz is used in Part 4 of BS 7671.

    It is introduced in Appendix 4, as a means of providing a "lookup value" that is at least Iz for the relevant conditions.

    It is one of the values in the tables in Appendix 4. The minimum value of Iz, when you combine all of the requirements in Part 4, must, by definition, be less than, or equal to, It ... but since It relates to discrete values of cross-sectional area S, it's quite unusual (statistically improbable) for the two to be identical, if you are mathematically pedantic.

  • There is no term as far as I am aware for the calculated value, just our 'It' has to be ≥ than that value.
    That has been a major part of my confusion.

    But ... that is the point. I responded a couple of minutes ago with the explanation that, I hope, makes sense:

    NO.

    The two are not directly related.

    Iz is used in Part 4 of BS 7671.

    It is introduced in Appendix 4, as a means of providing a "lookup value" that is at least Iz for the relevant conditions.

    It is one of the values in the tables in Appendix 4. The minimum value of Iz, when you combine all of the requirements in Part 4, must, by definition, be less than, or equal to, It ... but since It relates to discrete values of cross-sectional area S, it's quite unusual (statistically improbable) for the two to be identical, if you are mathematically pedantic.

  • The two are not directly related.

    Iz is used in Part 4 of BS 7671.

    It is introduced in Appendix 4, as a means of providing a "lookup value" that is at least Iz for the relevant conditions.

    It is one of the values in the tables in Appendix 4. The minimum value of Iz, when you combine all of the requirements in Part 4, must, by definition, be less than, or equal to, It ... but since It relates to discrete values of cross-sectional area S, it's quite unusual (statistically improbable) for the two to be identical, if you are mathematically pedantic.

    HOWEVER ...

    I will also throw this in.

    Because of the definition of the symbol in Part 2, once you have selected the cable cross-sectional area S, I can see that, if you have followed the selection criteria in Part 4, the actual selected cable Iz exceeds the minimum value Iz that is gleaned from the requirements of Part 4 (which is, of course, the purpose of the design exercise).

    BUT ...

    We then need to consider voltage drop, adiabatic, etc., and any of these may lead to a larger S.

    Which means that, in the general case, IZ ≥ It, which is what EIDG advises ?

  • I have not been following the discussion in its entirety, but I would like to clarify whether ( Iz ) is simply the value of ( It ) after applying the correction factors.

    NO.

    The two are not directly related.

    I'm not sure I agree.

    Iz is It multiplied by all the relevant correction factors (which is what I think AMK was suggesting).

    (unlike the usual calculation where we divide In or Ib by the correction factors - in effect converting our actual installation conditions to the conditions the tables are based on)

      - Andy.

Reply
  • I have not been following the discussion in its entirety, but I would like to clarify whether ( Iz ) is simply the value of ( It ) after applying the correction factors.

    NO.

    The two are not directly related.

    I'm not sure I agree.

    Iz is It multiplied by all the relevant correction factors (which is what I think AMK was suggesting).

    (unlike the usual calculation where we divide In or Ib by the correction factors - in effect converting our actual installation conditions to the conditions the tables are based on)

      - Andy.

Children
  • Hi Andy, yes all I was getting at was to take (It) from the regs, multiply by the correction factors to give you (Iz) So the cable could one carry the value of (It) but after applying derating factor s can now only carry a new value known as (Iz)