It and Iz
Im getting a bit confused with It and Iz, and which is out final value when calculating cable size
It  - the value of current tabulated in this appendix for the type of cable and installation method concerned, for a single circuit in the ambient temperature stated in the current-carrying capacity tables
Iz -  the current-carrying capacity of a cable for continuous service, under the particular installation conditions concerned.
In =32  Ca 0.87
so    It ≥  32 / 0.87
It ≥ 36.78A
Look up tables in BS 7671  clipped direct (c) one  2 core cable
4mm=36A
6mm= 46A
So we go with 46A
So our It (Tabulated value we look up) is 46A and we will use a 6mm2 cable
So what is Iz?
Iz ≥ In ≥ Ib  understand the relationship
Now Iz = It x correction factors.
Iz = 46 x 0.87 =  40.02A  which is greater than In (32A) so thats OK
But we got a value of 36.78 A when applying correction factors to In
We also have this formula...
It ≥ Iz / correction factors
40.02 / 0.87 = 46
We end up with the same number.
We have a calculated value of 36.78A  in the book the cable choice is 6mm which is rated at 46A
I'm struggling to see what we would call our final cable choice? Its not Iz , but the description (continuous service) makes it sound like it is
What is Iz
Hope that make some sense
Its based around this IET article
electrical.theiet.org/.../appendix-4-of-bs-7671.pdf
  • I think Graham was just saying the current carrying capacity of a cable (Iz ≥ Ib) is just one of several points that have to be considered when designing a circuit - other factors such as achieving a certain loop impedance, or required maximum voltage drop, may well require a larger cable than CCC consideration alone would suggest.
    Well, that, plus the important fact that it's not as simple as looking up the current-carrying capacity from a table in Appendix 4, given the cross-sectional area and cable type, and bingo, the value you look up (It) is equal to Iz. because it may be subject to factors such as grouping etc. that are not accounted for in the Tables themselves.
    Slightly confusingly though, it is NOT ALWAYS true that, when you go through the selection process in Appendix 4, at the point you choose a csa from the value of "minimum It" you have calculated considering the grouping factors, the value of It you choose from a table in Appendix 4, in order to be greater than or equal to the calculated minimum It, is Iz regardless of  have to increase S (as  says). This is because, when you apply correction factors, the tabulated value (you look up) drops down to IZ.
    More simply ... it's not a two-way process.