It and Iz
Im getting a bit confused with It and Iz, and which is out final value when calculating cable size
It  - the value of current tabulated in this appendix for the type of cable and installation method concerned, for a single circuit in the ambient temperature stated in the current-carrying capacity tables
Iz -  the current-carrying capacity of a cable for continuous service, under the particular installation conditions concerned.
In =32  Ca 0.87
so    It ≥  32 / 0.87
It ≥ 36.78A
Look up tables in BS 7671  clipped direct (c) one  2 core cable
4mm=36A
6mm= 46A
So we go with 46A
So our It (Tabulated value we look up) is 46A and we will use a 6mm2 cable
So what is Iz?
Iz ≥ In ≥ Ib  understand the relationship
Now Iz = It x correction factors.
Iz = 46 x 0.87 =  40.02A  which is greater than In (32A) so thats OK
But we got a value of 36.78 A when applying correction factors to In
We also have this formula...
It ≥ Iz / correction factors
40.02 / 0.87 = 46
We end up with the same number.
We have a calculated value of 36.78A  in the book the cable choice is 6mm which is rated at 46A
I'm struggling to see what we would call our final cable choice? Its not Iz , but the description (continuous service) makes it sound like it is
What is Iz
Hope that make some sense
Its based around this IET article
electrical.theiet.org/.../appendix-4-of-bs-7671.pdf
  • Sorry, This is the last I will post on this
    But this is a calculation using 2.4.0  (EIDG) equation first.
    Then the equations from BS7671
    I can provide this feedback, and perhaps some appropriate publications could be devised to fill the gap, if there is one?
    I really believe there is a gap and a need. Believe me I look and I can't find many publications that go into the little details, and give a full explanation and worked examples. There is a lot of regurgitation and old content out there.
    But I may of missed some so any suggestions gratefully accepted.
    And thank again for the help
  • Hello,
    I have not been following the discussion in its entirety, but I would like to clarify whether ( Iz ) is simply the value of ( It ) after applying the correction factors. I hope this is the case, as I have been in this profession for 30 years and this has been my understanding.
  • There is no term as far as I am aware for the calculated value, just our 'It' has to be ≥ than that value.
    That has been a major part of my confusion. Though I think I have it now, thanks to the advice in this thread.
    Be nice to give it a nameSlight smile
  • I have not been following the discussion in its entirety, but I would like to clarify whether ( Iz ) is simply the value of ( It ) after applying the correction factors.
    NO.
    The two are not directly related.
    Iz is used in Part 4 of BS 7671.
    It is introduced in Appendix 4, as a means of providing a "lookup value" that is at least Iz for the relevant conditions.
    It is one of the values in the tables in Appendix 4. The minimum value of Iz, when you combine all of the requirements in Part 4, must, by definition, be less than, or equal to, It ... but since It relates to discrete values of cross-sectional area S, it's quite unusual (statistically improbable) for the two to be identical, if you are mathematically pedantic.
    But ... that is the point. I responded a couple of minutes ago with the explanation that, I hope, makes sense:
    NO.
  • The two are not directly related.
    HOWEVER ...
    I will also throw this in.
    Because of the definition of the symbol in Part 2, once you have selected the cable cross-sectional area S, I can see that, if you have followed the selection criteria in Part 4, the actual selected cable Iz exceeds the minimum value Iz that is gleaned from the requirements of Part 4 (which is, of course, the purpose of the design exercise).
    BUT ...
    We then need to consider voltage drop, adiabatic, etc., and any of these may lead to a larger S.
    Which means that, in the general case, IZ ≥ It, which is what EIDG advises ?
    NO.
    I'm not sure I agree.
    Iz is It multiplied by all the relevant correction factors (which is what I think AMK was suggesting).
    (unlike the usual calculation where we divide In or Ib by the correction factors - in effect converting our actual installation conditions to the conditions the tables are based on)
  • Hi Andy, yes all I was getting at was to take (It) from the regs, multiply by the correction factors to give you (Iz) So the cable could one carry the value of (It) but after applying derating factor s can now only carry a new value known as (Iz)
  • Because of the definition of the symbol in Part 2, once you have selected the cable cross-sectional area S, I can see that, if you have followed the selection criteria in Part 4, the actual selected cable Iz exceeds the minimum value Iz that is gleaned from the requirements of Part 4 (which is, of course, the purpose of the design exercise).
    BUT ...
    Thank you for your continued help, but, I got a bit lost again, with the last comment.
    Don't want to be a pain, so no worries if you are done with this   Slight smile
    I can understand how Iz ≥ It when we  multiple by more than 1 , but generally its less than 1 so will be less.
    Say--- If we have our calculated value ≥It   and it is 27A, which suggests  2.5mm2 cable clipped direct.
    We do the volt drop and find because of the length of the circuit, the CSA of the 2.5 cable is too small, so we go up to 4mm2.
    In doing so the tabulated value for 4mm2 cable will also be a higher value, so It would be still greater than Iz. ?
    Sorry could you point out the section in EIDG that advises Iz≥It
    I've tried to explain in the attached sheet.
    Thank you.
  • Thank you for your continued help, but, I got a bit lost again, with the last comment.
    I think Graham was just saying the current carrying capacity of a cable (Iz ≥ Ib) is just one of several points that have to be considered when designing a circuit - other factors such as achieving a certain loop impedance, or required maximum voltage drop, may well require a larger cable than CCC consideration alone would suggest.
    Say for instance you had a 1A lighting load 1000m metres away - to achieve 3% v.d. (6.9V) you'd need a cable with a v.d. of 6.9mV/A/m or lower - which would probably mean 10mm² cable, even though 1mm² or even 0.75mm² would probably have been fine from just a current carrying capacity perspective.