The minimum distance from electrical supply equipment to gas pipes is noted as 150mm. Does anyone know if that info is listed / written in BS 6891 please? If not, does anyone know the standard where this info is recorded please?
The minimum distance from electrical supply equipment to gas pipes is noted as 150mm. Does anyone know if that info is listed / written in BS 6891 please? If not, does anyone know the standard where this info is recorded please?
Does anyone know if that info is listed / written in BS 6891 please?
Clause 8.4.2
Does anyone know if that info is listed / written in BS 6891 please?
Clause 8.4.2
Hi mate, apologies, I've forgotten your first name, but recognise you / your name from previous webinars completed, hope you're well.
Many thanks for the above info, can I assume you've taken that directly from BS 6891? If not, please advise where this is listed.
Thanks again, Tony.
Yes, above from BS 6891:2015+A1:2019
Kind regards,
Graham.
Hey Graham,
That's spot on mate, many thanks!
Best Regards,
Tony.
We're about to take you to the IET registration website. Don't worry though, you'll be sent straight back to the community after completing the registration.
Continue to the IET registration site