Fusing downstream using short smaller cable size - is it safe in industrial control panel?

Hi,

I am told (rightly or wrongly...) this is a grey area in both 7671 and low voltage assemblies regs, and just wondering if anyone can put the issue to bed. I have a customer with some LV industrial control panels, 100A fused isolator with 25mm main singles from isolator down to motor drive, but off the isolator terminals are also some short 6mm cables that go immediately to 1A fuses (within 3 or 4 inches). I am aware obviously this contradicts the requirement for conductor CSA rating to be >= upstream protective device rating, but also on the other hand have been told in the past this is fine to do as long as the under-rated cable is of sufficiently short length, there is no danger of mechanical damage to the cable, and the design load of its downstream circuit is suitably low - I believe all of those to be true in this case. So the opposite of de-rating I guess! Has anyone had a similar quandary in the past, and if so were able to find a definitive answer within the UK regs?

Entire circuit is enclosed within a steel control panel. Link to drawing and layout sketch of the installation below, unfortunately I don't have photos of the actual installation sorry.

https://drive.google.com/file/d/1ESq0gQdGBomQaqop18paDkeNScBu0HHn/view?usp=sharing

https://drive.google.com/file/d/1vUeMwEF0uvJExeX3vTxLTn-Obc5wI1iF/view?usp=sharing


Thanks in advance
Ed

Parents
  • For an everyday example, which is in both the OSG and the appendix in 7671, Ring Final Circuits with an unfused double socket spurred off the 2.5mm T+E ring. It will be protected, typically, by a 32 amp B type Circuit Breaker. The current carrying capacity of the 2.5mm T+E spur is around 26 amps at best, so looking at it without thinking, you would say it could overload the cable, so does not comply, however, the socket outlet and cable will be protected by the 13amp plug top fuses. So even if someone plugs in 2x 13 amp loads (very unlikely), the most current possible, (without a fault on the appliances) would be 26 amps, so the cable will comply.

    In the real world, the current drawn on that spur would never exceed 20 amps, and shouldnt exceed 13amps - the rating of the socket outlet.

    So yes, you can fuse an item downstream when it is tapped off a larger, unprotected supply, so long as the fault current can be satisfied - as Mike says above, most cables above 2.5mm will comply.

    433.2.2 is one of the relevant regs.

Reply
  • For an everyday example, which is in both the OSG and the appendix in 7671, Ring Final Circuits with an unfused double socket spurred off the 2.5mm T+E ring. It will be protected, typically, by a 32 amp B type Circuit Breaker. The current carrying capacity of the 2.5mm T+E spur is around 26 amps at best, so looking at it without thinking, you would say it could overload the cable, so does not comply, however, the socket outlet and cable will be protected by the 13amp plug top fuses. So even if someone plugs in 2x 13 amp loads (very unlikely), the most current possible, (without a fault on the appliances) would be 26 amps, so the cable will comply.

    In the real world, the current drawn on that spur would never exceed 20 amps, and shouldnt exceed 13amps - the rating of the socket outlet.

    So yes, you can fuse an item downstream when it is tapped off a larger, unprotected supply, so long as the fault current can be satisfied - as Mike says above, most cables above 2.5mm will comply.

    433.2.2 is one of the relevant regs.

Children
  • Hi Alan,

    Ed is referring to wiring within the industrial control panel. Whilst 7671 will be relevant to the cables coming in and going out of the panel, the construction of the panel, components and wiring within the panel must conform to BS EN60204. I won't list the safety standards and EMC standards etc, as these have no bearing on the issue raised.

    We often have to do this when manufacturing industrial control panels when we feed to a bus bar system, and then from the bus bar system to the individual circuits. We could be feeding a busbar system say with a 240mm wire which is never going to be able to feed a standard MCB as they only have terminals suitable for cable sizing up to 35mm or 25 with a bootlace ferrule fitted.

    Regards

    Pedro