DNO Connections to Buildings

Afternoon All

Quick 'simple' question hopefully someone has a simple answer to.

Why are DNO's (like UKPN, SSE etc.) adverse to providing buildings with more than a single incoming LV supply?

Are they concerned about risks/ regs, or is there another reason.

Would like to know.

Many thanks

Ade

Parents
  • I would support the use of higher voltages in large premises, 400/690 certainly and perhaps even 690/1k2

    In most large premises, lighting and/or electric motors are often a large part of the load, and lighting ballasts are available for 400 volts. All but the smallest electric motors tend to have 400 volt windings suitable for delta connection on 230/400 volt systems  or for star connection on 400/690 volts.

    The drawback is the need to still supply 230 volts single phase for loads that need it.

    690/1,200 is more problematic as equipment choice is more limited, and of course 1,200 volts is considered high voltage

Reply
  • I would support the use of higher voltages in large premises, 400/690 certainly and perhaps even 690/1k2

    In most large premises, lighting and/or electric motors are often a large part of the load, and lighting ballasts are available for 400 volts. All but the smallest electric motors tend to have 400 volt windings suitable for delta connection on 230/400 volt systems  or for star connection on 400/690 volts.

    The drawback is the need to still supply 230 volts single phase for loads that need it.

    690/1,200 is more problematic as equipment choice is more limited, and of course 1,200 volts is considered high voltage

Children
  • and lighting ballasts are available for 400 volts.

    Mercury (including fluorescent) lamps now banned, although other discharge lamps such as SON/SOX etc. will be available until at least 2027. However, as evidenced from street lighting, discharge lamps are being phased out for more energy efficient alternatives.

    Other technologies ... chiefly LED ... are taking over now.

  • LED is not always low power if you have enough of them. This driver for example can put up to 400V across a string of LEDs taking a touch over a couple of amps per string
    Pricey, but you only need one per lighting tower to turn night into day.
    (and so the generator at the bottom runs for days.)
    Eye damage at close range really is a consideration, the lights should only be on full power once  the pole is up.

    the lumens per watt are about twice as good as the SON type if driving this sort of thing


    Mike

  • LED is not always low power if you have enough of them.
    the lumens per watt are about twice as good as the SON type if driving this sort of thing

    Agreed ... isn't stopping the charge to LED though.

    I was chiefly trying to point out that, for good or bad, the '400 V ballast' isn't really the way things are heading.

  • Except that the LED driver I linked to has a 180- 585 volt input range, to allow use as a 400v fitting, and also  leaving me wondering if the design  aimed for 600V and missed;-)