Wiring regulations and their application to optical fibre in the home.

I understand that telecoms wiring is subject to section 521.10.202 of BS7671:2018. Cat 5 ethernet cable is just as capable of causing entanglement of emergency service personnel as a mains power cable. I wanted to know if the tensile strength of the cable in question may be taken into consideration or if any provision is made for very light cable?  Some of the single core buffer fibre I am working with has the tensile capacity of sewing cotton and crumbles in fire.  Even very small metal clips do not offer the clamping force needed to support the vertical runs and I wanted to use some intumescent caulking.

Parents
  • Why would wiring regulations apply to glass fibres that don't even conduct electricity?

    Because Coroner's Rule 43 letter following the inquest into the Shirley Towers fire recommended it?

    To quote item 6 (my highlight):

    6 It is recommended that Building Regulations are amended to ensure that all cables, not just fire alarm cables, are supported by fire-resistant cable supports. This could be achieved by an amendment to BS 7671 (2008) Institute of Electrical Engineers Wiring Regulations.

    A copy of the letter is available in the following Report, and you can see the above item 6 on Page 5: https://www.shropshirefire.gov.uk/sites/default/files/11-coroners-rule-43-letter.pdf

    ome of the single core buffer fibre I am working with has the tensile capacity of sewing cotton and crumbles in fire.  Even very small metal clips do not offer the clamping force needed to support the vertical runs

    That might lead to it being unsuitable for some areas without a suitable support system ... I see the issue, and there's an open question about whether it might (or might not) cause entanglement.

    Have you asked the advice of the manufacturer, importer or distributor ?

  • Thanks all

     

    The supplier provides guidance for installation for compliance edition 18 and from that point of view it is not an issue. We have a compliant solution. My question was broader in the sense that entanglement, as serious as it is, has a lower limit. The fibre I am referring to is 900 microns in diameter and has no strength member, it can be broken by hand with little effort.  As we switch from copper lines to optics would I wanted to know if this had been considered already or might in the future there may be dispensation for single lines with a breaking force of some yet to be defined limit. Mechanical clamping of fibres of this nature can lead to damage of the fibre and intumescent adhesives may offer an alternative.

Reply
  • Thanks all

     

    The supplier provides guidance for installation for compliance edition 18 and from that point of view it is not an issue. We have a compliant solution. My question was broader in the sense that entanglement, as serious as it is, has a lower limit. The fibre I am referring to is 900 microns in diameter and has no strength member, it can be broken by hand with little effort.  As we switch from copper lines to optics would I wanted to know if this had been considered already or might in the future there may be dispensation for single lines with a breaking force of some yet to be defined limit. Mechanical clamping of fibres of this nature can lead to damage of the fibre and intumescent adhesives may offer an alternative.

Children
  • From my experience at least it's normal practice to run this type of fibre in some sort of protective tube? Probably still an argument that the tube will melt before a plastic clip fails. If there were a large number I can see an argument for support that will not suffer from premature failure. But for one or two i would probably use engineering judgement. There is nothing to say clips have to hold things tightly, they just have to prevent collapse.

  • As we switch from copper lines to optics would I wanted to know if this had been considered already or might in the future there may be dispensation for single lines with a breaking force of some yet to be defined limit.

    That's a good question ... individual runs are of course a different beast to bundles.

    Are there other safety issues for the public with easily-breakable fibres though?