Hello
So a ring final has
So table 4C1
Hello
Rings are an odd one. The tables are really intended for cables that can carry their full load - but with a ring you've got two 20A(+) cables that can only carry 32A between them (e.g. one at 20A and the other at 12A or both at 16A, or any other combination you choose), so from the physics point of view, it's really just one-and-a-bit circuits.
That said, in domestics, most circuits almost never carry anything like their full rated current and even when one or two circuits occasionally do, the rest almost certainly won't (with a few notable exceptions, like a house full of night storage heaters) - so often grouping factors are downplayed to almost the point of being ignored in domestics (even DNOs reckon on each house drawing no more than 10A on average). I think one version of the OSG effectively said don't worry about grouping for up to 6 normal domestic circuits bunched together (high power, long duration, loads like storage heaters and immersions excepted). EVs and heatpumps might shift the goalposts a bit - but still the majority of domestic circuits carry negligible loads most of the time.
Things can be quite different in some commercial or industrial situations where several rings might all be carrying close to full load for much of each day.
The multi-core cable vs circuit debate is an old one - originally it was circuits so you could use the same tables whether you had singles in conduit or multi-core cables, but neither seem that clear where you can have conductors in parallel, including multi-core cables in parallel, or situations where conductors go down and back up the same path (e.g. looping into switches or sockets). Really you've looking for how many times as much heat will be created by the cables in your particular situation, compared with the reference installation method - so some judgement is needed. (Remember appendix 4 is only informative, you don't have to follow it to comply with BS 7671).
- Andy.
Rings are an odd one. The tables are really intended for cables that can carry their full load - but with a ring you've got two 20A(+) cables that can only carry 32A between them (e.g. one at 20A and the other at 12A or both at 16A, or any other combination you choose), so from the physics point of view, it's really just one-and-a-bit circuits.
That said, in domestics, most circuits almost never carry anything like their full rated current and even when one or two circuits occasionally do, the rest almost certainly won't (with a few notable exceptions, like a house full of night storage heaters) - so often grouping factors are downplayed to almost the point of being ignored in domestics (even DNOs reckon on each house drawing no more than 10A on average). I think one version of the OSG effectively said don't worry about grouping for up to 6 normal domestic circuits bunched together (high power, long duration, loads like storage heaters and immersions excepted). EVs and heatpumps might shift the goalposts a bit - but still the majority of domestic circuits carry negligible loads most of the time.
Things can be quite different in some commercial or industrial situations where several rings might all be carrying close to full load for much of each day.
The multi-core cable vs circuit debate is an old one - originally it was circuits so you could use the same tables whether you had singles in conduit or multi-core cables, but neither seem that clear where you can have conductors in parallel, including multi-core cables in parallel, or situations where conductors go down and back up the same path (e.g. looping into switches or sockets). Really you've looking for how many times as much heat will be created by the cables in your particular situation, compared with the reference installation method - so some judgement is needed. (Remember appendix 4 is only informative, you don't have to follow it to comply with BS 7671).
- Andy.
Thank you also , you reply has covered a lot of my questions.
We're about to take you to the IET registration website. Don't worry though, you'll be sent straight back to the community after completing the registration.
Continue to the IET registration site