Overload protection - Regulation 433.1.201and BS 88 fuses

Regulation 433.1.201 indicates that a BS 88-2 or BS 88-3 fuse, with a rated current (In) not exceeding the current carrying capacity of the circuit conductors, will comply with condition (iii) of Regulation 433.1.1. [i.e. the current (I2) causing effective operation of the protective device does not exceed 1.45 times the current carrying capacity of the circuit conductors].

However, the product standard for those fuses (BS EN 60269-1:2007+A2:2014), along with Table 4.1 of the Electrical Installation Design Guide, gives If (I2) as 1.6 In, which clearly exceeds the 1.45 of Regulation 433.1.1. Furthermore, the conventional fusing time for fuses rated in excess of 63 A is greater than 2 hours, as opposed to 1 hour for a BS EN 60898 circuit breaker, which would surely increase the likelihood of a cable overheating under overload conditions.

Does anyone have an insight into this apparent inconsistency, or am I misunderstanding something?

Geoff

Parents
  • I'm fairly sure the correction factor of 1.6 is for a re-wirable fuse. (Not a BS-88 HRC fuse.)

  • I'm sorry - I've out clevered myself - I wish I knew how to delete a silly reply - but I dont - 0.725 is the correction factor for re-wireable fuses, not 0.6.....

    Please pass over my above reply. 

    I've just checked p425 5.1.1 - this references back to 433.1.201 - does this help? Probably not and I'd need access to the product standard.........

Reply
  • I'm sorry - I've out clevered myself - I wish I knew how to delete a silly reply - but I dont - 0.725 is the correction factor for re-wireable fuses, not 0.6.....

    Please pass over my above reply. 

    I've just checked p425 5.1.1 - this references back to 433.1.201 - does this help? Probably not and I'd need access to the product standard.........