Concentric cable, consumer side.

A house converted into three flats probably 20+ years ago.
TNCS supply. Earthing conductor onto the MET

Meter tails in to three 60A  switch fuses 
Concentric cable ran from the switch fuses to the three flats consumer units.
Solid Aluminium core. Decent size must be 25mm  multi stranded copper neutral , haven't counted  but lots.
Separate 16mm earth ran to each flat from the DNO labeled MET.

Replacing the board in one of the flats.


My concerns

Cable ran in the fabric of the building, No earthed protection, No RCD protection, Tails not double insulated, dissimilar metals
But..
Cable all as clean as the day it went in, aluminium clean and bright, better than twin and earth, which has been pointed out on other searches.

Is this OK for continued use?