Concentric cable, consumer side.

A house converted into three flats probably 20+ years ago.
TNCS supply. Earthing conductor onto the MET

Meter tails in to three 60A  switch fuses 
Concentric cable ran from the switch fuses to the three flats consumer units.
Solid Aluminium core. Decent size must be 25mm  multi stranded copper neutral , haven't counted  but lots.
Separate 16mm earth ran to each flat from the DNO labeled MET.

Replacing the board in one of the flats.


My concerns

Cable ran in the fabric of the building, No earthed protection, No RCD protection, Tails not double insulated, dissimilar metals
But..
Cable all as clean as the day it went in, aluminium clean and bright, better than twin and earth, which has been pointed out on other searches.

Is this OK for continued use?

Parents
  • It would probably be fine for continued use in practice. Seems to NON compliant with regulations though.

    All live conductors are now required to be insulated and sheathed. In concentric cable as described the neutral is merely enclosed in the outer sheath and is not insulated

  • I suppose you could declare it a PEN rather than N and comply with BS 7671 (section 543.4) - although you'd probably want to avoid DP switching upstream, and of course deem it to be part of the BNO's installation rather than the consumer's to meet the ESQCR. But again puts it in context as far as actual safety is concerned.

       - Andy.

  • I suppose you could declare it a PEN rather than N and comply with BS 7671 (section 543.4) -

    I did think about this (it being in the BNO network), but the provision of earthing alongside it made me think again (you can't have PEN downstream of the PEN-PE split in BS 7671, or IEC 60364 for that matter).

    But, if the 16 sq mm is bonding (not cpc) ... ??? Without seeing the installation, at this point, we'd be guessing?

Reply
  • I suppose you could declare it a PEN rather than N and comply with BS 7671 (section 543.4) -

    I did think about this (it being in the BNO network), but the provision of earthing alongside it made me think again (you can't have PEN downstream of the PEN-PE split in BS 7671, or IEC 60364 for that matter).

    But, if the 16 sq mm is bonding (not cpc) ... ??? Without seeing the installation, at this point, we'd be guessing?