Checking if 1.0mm cpc on 2.5mm cable is acceptable for EICR and where the limit is

Just want to check my calculations and conclusions are correct.
(been meaning to do this for a while)

Checking if a 2.5/1.0mm cpc is acceptable on a 32A  ring final for an EICR.

In this example looking at data for MK 32 A MCB MK data sheet

In the graphs I am assuming the horizontal is PSCC/PFC. In my example I have a PFC of 700A, therefore I2T = about 5000 A/sec

Energy withstand for 1.0cpc  K2S2 = 115*115 * 1.0 = 13,225

I2t needs to be less than K2S2

5000 < 13,225  therefore I am ok.

If I look at the graph and find I2t of 13,000 it looks like I am ok for pscc/pfc  up to about 3K, bit difficult to read with linear graduation on a log scale.

In reality the B type actually switches in 10msec with 5 * rated current rather than the 100msec typically used in calculations.


Parents
  • Part P of the Building Regulations came into effect 1st January 2005 and the original version had “useful information” in it, including guidance about 2.5 mm twin and earth cable with a 1.0 mm CPC.



    https://kentbuildingcontrol.co.uk/pdf/approved-document-p-2005.pdf

    The general consensus after doing those calculations twenty odd years ago was that a BS60898 B32 MCB could be okay, a BS3036 30-amp fuse will probably be inadequate, but the best option is probably the BS1361 30-amp fuse.

    As the original Part P said there’s various options regards upgrading the cable and/or the consumer unit, depending on the circumstances, not a set answer.

    But, a lot has changed in the last twenty years and it’s unlikely that anyone will use a BS1361 fuse in a consumer unit to protect a socket ring circuit these days, leaving a less favourable choice the MCB.

Reply
  • Part P of the Building Regulations came into effect 1st January 2005 and the original version had “useful information” in it, including guidance about 2.5 mm twin and earth cable with a 1.0 mm CPC.



    https://kentbuildingcontrol.co.uk/pdf/approved-document-p-2005.pdf

    The general consensus after doing those calculations twenty odd years ago was that a BS60898 B32 MCB could be okay, a BS3036 30-amp fuse will probably be inadequate, but the best option is probably the BS1361 30-amp fuse.

    As the original Part P said there’s various options regards upgrading the cable and/or the consumer unit, depending on the circumstances, not a set answer.

    But, a lot has changed in the last twenty years and it’s unlikely that anyone will use a BS1361 fuse in a consumer unit to protect a socket ring circuit these days, leaving a less favourable choice the MCB.