Checking if 1.0mm cpc on 2.5mm cable is acceptable for EICR and where the limit is

Just want to check my calculations and conclusions are correct.
(been meaning to do this for a while)

Checking if a 2.5/1.0mm cpc is acceptable on a 32A  ring final for an EICR.

In this example looking at data for MK 32 A MCB MK data sheet

In the graphs I am assuming the horizontal is PSCC/PFC. In my example I have a PFC of 700A, therefore I2T = about 5000 A/sec

Energy withstand for 1.0cpc  K2S2 = 115*115 * 1.0 = 13,225

I2t needs to be less than K2S2

5000 < 13,225  therefore I am ok.

If I look at the graph and find I2t of 13,000 it looks like I am ok for pscc/pfc  up to about 3K, bit difficult to read with linear graduation on a log scale.

In reality the B type actually switches in 10msec with 5 * rated current rather than the 100msec typically used in calculations.


Parents
  • But the calculation seems to ignore the current split? 

  • hmm  in the worst case it could be  a spur couldn't it.... I suspect also in many cases of existing circuits , we probably don't really care too much if we manage to drill into a bit of old cable, and if in the process of going bang we now have to change a bit more length of it than just the little bit that got drilled or nailed.  

    The temperature assumptions that underpin the upper 'damage/no damage' limit to the PVC in the adiabatic equation only really became important once we moved away from rubber covered cables - in the older cases, where the onset of thermal degradation was much less clear, also the life of the cable even at room temp was more limited.

    Mike

  • hmm  in the worst case it could be  a spur couldn't it..

    Doh! ….it was Saturday night when I responded but I can’t even blame the beer since I have been off it for quite a while!