Self-testing emergency lights BS 5266-1:2016

I just need confirmation as I couldn't find the info in the BS5266 book.

If I choose self-testing emergency lights for my project do I still need an "old fashioned" emergency lighting test key switch to do regular monthly or annual tests?

Self-testing lights are smart enough to indicate visually or audibly once the problem has been detected so I guess it is not necessary to have test key switches as well but some places still do it, why?

Parents
  • No, if the self-test system can perform the monthly and annual tests then a key-switch is not required. Self test systems should be in accordance with BS EN 62034.

    Clients might still request one to facilitate a manual test for spot checking the auto system or because "that's what we always have" (not a great reason but hey, if they want it and will pay for it, it's their choice).

  • Is the 3 hour duration test only required once a year? Or is it required more frequently? Am trying to assist a charity run building but am not a E/light specialist. I gather the quick on/off check is required monthly but don't know about the 3 hr one. On the fittings I have replaced, I always disable the self-test jumper setting because they are used to using the key switch test points already provided, and asking them to check for red/yellow/orange indicator lights would only complicate the issue.,

Reply
  • Is the 3 hour duration test only required once a year? Or is it required more frequently? Am trying to assist a charity run building but am not a E/light specialist. I gather the quick on/off check is required monthly but don't know about the 3 hr one. On the fittings I have replaced, I always disable the self-test jumper setting because they are used to using the key switch test points already provided, and asking them to check for red/yellow/orange indicator lights would only complicate the issue.,