Substation Entry- Short section of cable in duct

Hi I am in the middle of a design for a new substation and one of the supplies is circa 150m long and will run for 146m on a ladder in free air. The final 4m will be routed underground into the substation through a duct then the substation trench into the LV switchboard. 

when calculating for this if I say the cable is just on the ladder then I need a single 240mm2 cable, however if I say it’s buried in ducts then the cable requirement becomes 3 x 300mm2 cables in parallel which seems extreme in practical sense. 

does anyone have any thoughts on this or experience of a similar situation and how to comply with BS7671 whilst still being practical.

Parents
  • It might be worth accepting the use of oversized cables for the entire run. This will save significant money at todays electricity pries, especially if the load is a long hour one.

    I suggest calculating the losses and the annual cost thereof, and putting the upsized cable to the client as an option.

Reply
  • It might be worth accepting the use of oversized cables for the entire run. This will save significant money at todays electricity pries, especially if the load is a long hour one.

    I suggest calculating the losses and the annual cost thereof, and putting the upsized cable to the client as an option.