Suppose I have an inverter 150m from intake. When delivering output, how does it establish and continue to monitor the reference grid voltage?
The IET is carrying out some important updates between 17-30 April and all of our websites will be view only. For more information, read this Announcement
Suppose I have an inverter 150m from intake. When delivering output, how does it establish and continue to monitor the reference grid voltage?
As mapj1 says, the inverter operates based on the voltage at its terminals, and knows the current it's driving out (so knows the 'overdrive voltage' to provide.
The reason for the 1 % volt-drop (or what is in effect "voltage rise" over the grid voltage) is that you can get the situation where the inverter is dropping out repeatedly because it has an upper "overvoltage trip" threshold according to G98/G99, if it has to drive over too long a line to reach the grid.
As mapj1 says, the inverter operates based on the voltage at its terminals, and knows the current it's driving out (so knows the 'overdrive voltage' to provide.
The reason for the 1 % volt-drop (or what is in effect "voltage rise" over the grid voltage) is that you can get the situation where the inverter is dropping out repeatedly because it has an upper "overvoltage trip" threshold according to G98/G99, if it has to drive over too long a line to reach the grid.