Insufficient crimps on lug barrel

Stranded, large-ish aluminium conductor cables buried direct terminated onto equipment terminals with bimetallic lugs several years ago. It has recently been noticed that that the electrical contractor made three out of six crimps on the marked barrel (I’m guessing they thought they had a wider die), but otherwise good workmanship. No signs of stress at terminations.

What’re your thoughts on the best way forwards?

One option would be to make the remaining crimps in the 1st, 3rd and 5th position… since that’s then out of order could that do more harm than good, or is it better done the wrong order and over time than not at all? The cables are buried so assume not enough play for starting again.

Parents
  • If it has been in use for some years, and shows no signs of heat stress or damage I might be inclined to accept continued use "as is"

    Ongoing temperature monitoring by means of temperature sensitive labels might be prudent.

  • Good shout on the labels: I believe the cables are oversized for volt drop so shouldn’t get anywhere near a limiting temperature unless something’s awry