AMD 4 DPC - new section 545 - functional earthing
Has anyone had a look at the proposed new section 545 (functional earthing) in AMD 4 DPC?
At first glance, it seems rather confusing (to little heads like mine at least). I can see the general point of trying to keep protective conductor currents (whether due to normal conditions or faults) from flowing along functional earthing conductors - so AFARP connect to the protective earthing system at one point only - at least for each "cluster" of interconnected equipment.  It seems to be rather prescriptive though - e.g. "If there are multiple functional bonding conductors present in the electrical installation, a separate main functional earthing terminal (MFET) shall be installed for ease of connection for these conductors. The main functional earthing terminal shall be connected to the main earthing terminal only once." - so if I had two clusters of equipment at opposite ends of a large installation, would this prevent me connecting each cluster independently to a local PE (say a nearby DB) but rather have to run all the functional earthing/bonding conductors back to one central MFET? It doesn't seem to be a good fit with the proposed 545.2 "The main functional earthing terminal MFET and the MET may be combined" nor the methods described in 444 (e.g. Fig A444.2).
Or have I missed something obvious? (again)....
  • Hi Andy. In my view, running all functional earthing conductors back to a central MFET could be more cumbersome and costly in most instances. The existing method in Figure A444.2, seems much easier to apply and clearer than the proposed methods in section 545.
    -Andrew
  • Or have I missed something obvious? (again)....
    The earthing topologies, star point vs mesh (multiple-bonding) are discussed in BS IEC 61000-5-2, and are well understood.
    Agreed ... in most cases. There are some cases, however, where it may be relevant to control voltages (and currents) in the FE system.
    The general considerations in selecting approaches are:
    • Common-mode vs differential-mode interference or "noise".
    • Bandwidth and cutoff frequencies (of EMI or the victim system).
  • I've been ponding this one and realized I don't really understand what a functional bonding conductor - as distinct from a functional earthing conductor - would do. Having grown up in the days of RS-232 and earth break recall on PBX phones, I think I understand the idea of signal lines using earth as a return (or 0V reference) conductor - so those "GND" lines would be functional earths I guess. So what would a functional bonding conductor do that would be different to a functional earth conductor? Back in LV land we use bonding conductors to reduce potential differences for shock protection purposes, especially during faults, but functional systems don't have to worry about shock protection (the PE system takes care of that). I know we sometimes reinforce or shunt thin functional earth conductors with large parallel (by-pass) conductors - are those thought of as bonding conductors, or just parallel/low-impedance FE conductors?
  • My understanding is as you suggested that the shunt conductors serve to provide parallel, low-impedance paths for functional earthing conductors. Are the bonding conductors intended to ensure that different parts of the system maintain the same potential, thereby preventing interference throughout ?
  • The problem is much weirder than that - for cables carrying high speed/ high frequency signals, the currents that represent the start of the 'message' have not actually come out the far end, while the next cycle(s) of the message is/ are being stuffed in, so if you had many little volt-meters along the line at intervals, and could magically take a snapshot of them all at once, they would all be reading different things at any moment.   The same applies to return paths, and very odd and unpleasant things happen if the difference in time between the 'out' and 'return' paths for the current are offset in time by more than a small fraction of a symbol period/cycle. (100m cable of 100base T is a good example, where a very short packet may be completely 'in flight' while transmission at the start has already finished, and the reception at the far end has not yet begun..)
    An earth wire that is too long is actually worse than none at all, especially at frequencies where it is more than a quarter cycle long.
    Earthing for such systems may contain RF traps and ferrite beads and things to encourage signal currents to go the right way whilel leaving the DC/50Hz path intact (those bumps on USB leads and video cables do that)
    To the outsider this often looks not dissimilar to magic, though it is fully logical, it is far from simple and full of exceptions.
  • Thanks all. I think you're reinforcing my original thought - that in many cases bringing all FB conductors back to a single per installation MFET could be counter productive. Perhaps similar to the idea of deliberately connecting bathroom supplementary bonding back to the MET - it's as likely to skew things by puling down one corner as have any reliable benefit. Maybe they mean A FET per cluster rather than a MFET per installation, but the words don't seem to say that to me, and even then it doesn't always seem appropriate (e.g. where the cluster has its own mesh). It all feels a bit unclear for a "shall" regulation.