Using the earthing system of one building to another

I have a question about earthing systems. 

In this scenario, I have a main commercial building that is fed from a new substation and is likely (as expected) to be a TNCS arrangement with a neutral earth link in the main LV switch panel for the customer.  From this LV switch panel, it feeds another building as part of the sub-mains distribution, probably close to 80m away. The schematic shows parallel multicore cables supplying the building with a separate CPC and, in addition to this, a separate bond to a dedicated earth bar (i.e. 1No CPC and 1No bond). I presume this is acceptable, and even though this may look like a TNS in the second building, it is an extension of the TNCS with the CPC going back to the first building's mains switch panel where the neutral earth link is......

What are people's thoughts? 

Parents
  • The main bonding of the second building, and a protective bonding from the MET of the second building back to the MET of the original building, will still need to be sized in accordance with Table 54.8 using the CSA of the distributor's PEN conductor.

Reply
  • The main bonding of the second building, and a protective bonding from the MET of the second building back to the MET of the original building, will still need to be sized in accordance with Table 54.8 using the CSA of the distributor's PEN conductor.