IEC 62271-200 - Breaker rack-in and closure

Good morning everyone!!!
Do any of you have the IEC 62271-200 standard and can help me clarify a doubt?
During an inspection of a 6.6 kV metal-enclosed switchgear, it was found that: in the extracted breaker position it is possible to unlock and open the front door of said breaker.
At the moment when you want to insert (rack-in) the breaker, the only security is a “pin” on the rear door which, when placed on the breaker, goes to unlock the truck of the breaker and allows its rack-in and closure under voltage. All, as you may have guessed, without a closed+locked hatch control.

Does IEC 62271-200 explicitly prescribe that it cannot be possible to close a circuit breaker with an unclosed door?
Or that it is not possible to rack-in with door not closed?

Thanks to all who would like to help me

Regards

P.