I am planning to make a 110v circuit containing up to 10 x 16A 110V single sockets. The circuit is up to 100m long. Is 32A MCB type C and H07 4mm2 will be ok for it or I need to take into consideration of using RCBO instead and calculate voltage drop to size required cable properly?

Parents
  • First, why are there so many sockets please? If it is to enable machinery or tools to be used at different workstations (OR), it may be fine; but if it is to enable multiple machines to be used (AND), will you not overload the circuit?

    Second, a domestic ring depends upon the BS1362 fuse in every plug. How will you replicate that?

Reply
  • First, why are there so many sockets please? If it is to enable machinery or tools to be used at different workstations (OR), it may be fine; but if it is to enable multiple machines to be used (AND), will you not overload the circuit?

    Second, a domestic ring depends upon the BS1362 fuse in every plug. How will you replicate that?