Arc Fault Detection Device without rcd

one of our contractors has installed several Hagar ARM932U Arc Fault Detection Device.

After many enquires Hagar Technical confirm its only a MCB with AFDD.

The contractors insist its an rcbo as well , i put 550mA on an (RCD) Residual Current Device test  it did not trip.

this had made me wonder if others have come across such devices and where they are designed to be installed to?

Parents
  • You are missing a “R” in the catalogue number. Should be ARR932U for the rcbo feature. £198 a pop according to Hager website prices, small wonder they are slow to catch on. 

Reply
  • You are missing a “R” in the catalogue number. Should be ARR932U for the rcbo feature. £198 a pop according to Hager website prices, small wonder they are slow to catch on. 