RCD trip time on TT 3 Phase system 0.2 or 0.07

Hi All,

I'm going round in circles and confusing my self, looking at Table 41.1 max disconnect times.

For single phase system 0.2 seconds but for 3 phase would it be 0.2 or 0.07 seconds, its so simple yet I'm unsure.

I'd say 0.2 seconds because it's 230V to earth not line to line..

if it is 0.2 seconds what scenarios would the other two columns be used in ( 230V < Uo < 400v ) and ( Uo > 400V )

Parents
  • BS 7671 (over) simplifies this, by saying that you need to look for a Zs (that is, fault to Earth) per Table 41.5 in TT systems, where RCDs are used for ADS.

Reply
  • BS 7671 (over) simplifies this, by saying that you need to look for a Zs (that is, fault to Earth) per Table 41.5 in TT systems, where RCDs are used for ADS.