UPS Manual Bypass

Hi everyone

I have a customer that wants a manual bypass for their UPS

Currently there is nothing, the feed goes straight through the UPS and to a sprinkler pump via a control panel.

They have confirmed that they just want it for manually switching over to mains supply if the UPS fails.

The circuit isn't critical and can be interrupted to switch over to mains.

Their budget is tight as they are a charity.

I am thinking of just using a 3 position changeover switch. 

https://www.cef.co.uk/catalogue/products/1780467

Any thoughts please?

Parents Reply Children
  • Nicely put! :-)

    I can see the point. If you have to take the UPS offline for maintenance, can you maintain the mains supply in the meantime?

    I do not quite understand, "the feed goes straight through the UPS". Surely the mains and UPS should form the legs of a Y with the stem supplying the sprinkler system. Then if either is offline, a supply is maintained. Your 3-way switch needs to provide supply 1 on, supply 2 off; supply 2 on, supply 1 off; supply 1 and supply 2 on.

  • supply 1 and supply 2 on.

    If that means effectively shorting the UPS output to the mains supply, I'd suggest avoiding that situation. Firstly unless the UPS is designed for parallel operation, there's no guarantee its a.c. output is synchronised to the mains (with a resulting flash, bang and magic smoke escape) when the switch is closed. Also you really don't want local generation potentially feeding back into the mains both for isolation and load reasons.

    Another alternative to a manual change-over switch might be an automatic transfer switch.

       - Andy.

  • A good point. I was assuming that the UPS fires up only if mains power is lost, and closes down when mains power is restored.

  • This is a critical clarification...

    If it's irrigation, why the UPS?
    If it's fire suppression:  UPS may be unnecessary depending on the category of the system.

    Either way, I'd steer clear of 3-position switch. Isolation from supplies should probably be via lockable isolators.

    If it is for fire suppression, are all your cables fire rated?