I have a wylex split consumer unit with two WRS80/2 30mA RCDs feeding a series of final circuits including ring mains and lighting. These are fed by NHXB32 and NHXB6 MCBs respectively. Currebt system works fine and there are no earth faults on the system.
I have fitted RCBOs in place of the MXCBs as follows:
- NHXSBS6B on the lighting
- NHXSBS32B on the ring mains
- In place of the WRS80/2s I have fitted WRDMT100/2 time delayed RCDs for discrimination.
Ring main RCBOs work fine. The RCBO on the lighting circuits trip immediately I switch the breaker on. This happens on all three lighting circuits.
- Lighting circuits have a mix of LED and halogen lamps. Total LED load on each is around 120W (12x6W)
- Each RCBO is wired correctly and the correct meutrals are wired into the RCBO. The neutral flying lead is on the neutral bar and the functional earth is connected to the earth bar.
Can anyone suggest why the RCBO is tripping? My only suggestio wuld be a borrowed neutral. Given all three lighting circuits use the same neutral bar and the problem has only arisen since I fitted RCBOs then I'm wondering if neutrals have been shared between circuits (would not have been an isue before as all three circuits shared the same WRS80/2 RCDs.