How to verify the size (and therefore current carrying capacity) of an old mineral insulated submain cable?

I have a client who's 1 bedroom flat is now fully electric (shower, heating, hot water, etc.) and wants to install further appliances such as a largeish (5 ring) induction hob. The flat is supplied via an old mineral insulated cable. It is 2 core with the sheath as the main earth - glanded into an old rusty Ryefield board. From previous cables Ive seen and verified it looks bigger than a heavy duty 2 core 10mm.. however the only markings i can see on the pots (or glands?) are what looks like the numbers 590. The inner cores where exposed are marked on the over sleeving with 0225.

Not sure if this is an imperial size, or if the 590 is not relevant to the size. Basic concern is if it is only a 10mm then I believe the flat could potentially overload the submain cable especially with the additional induction hob.
The Ryefield cutout fuse is marked 100A on the carrier, but I haven't opened this up yet to confirm the fuse size.

Any advice or pointers in the right direction really appreciated.

As a newish electrician still very inexperienced with mineral insulated cable work. as a side note would be good actually to find somewhere to gain more experience with it.

Jonathan

Parents
  • You could try some manufacturer's data sheets - e.g. https://www.aeicables.co.uk/uploads/6/2021-01/7b5785642eac225b6c775e870dadbd14.pdf - you might have to interpolate a bit if it is imperial size of course.

    Or just measure the actual conductor diameter and work it out (A=π(d/2)²)  (I've got a plastic vernier caliper similar to this that seems to works well enough for me)

    Or someone else here might recognise those part numbers...

       - Andy.

  • I've got a plastic vernier caliper similar to this

    Andy, shame on you! Where is the Vernier scale please?

    I admit that I find a pair of dial callipers easier to use, and electronic ones even better.

    That said, measuring the conductors would be helpful. If the circuit is isolated, why not use a good quality metal device?

  • Thanks Andy.
    Going to have a look for some calipers to measure cables in future where needed.