Protected corridors and ELV cabling

Hi, Does anyone know whether the 422.2.1 requirements for compliance with BS EN 60332-3 fire propagation (bunched cables) also applies to ELV cables including cat 6 cables or is is this requirement limited to LV cable?

Parents
  • Yes, because it's about the smoke etc. produced in a fire impeding escape etc.

    BS 7671 applies to ICT cables as well as power/control (as required by BS 6701). This includes optical fibre cables.

Reply
  • Yes, because it's about the smoke etc. produced in a fire impeding escape etc.

    BS 7671 applies to ICT cables as well as power/control (as required by BS 6701). This includes optical fibre cables.