I need some advice about running power to flower beds and a shed using 2.5mm NYY-J cable and whether it complies with BS.

The cable will feed from the consumer unit using a 16A MCB to an outside connection box to feed both sides of plants (as diagram provided).

The cable size and MCB were chosen based my needs and the limited power to be drawnThe cable will not be buried but will run along the perimeter of my fence on top of a 20mm pipe (not plastic conduit) secured either with plastic or metal cable ties.

The pipe will secured the concrete fence posts150mm above the ground heavy-duty saddles.

Each bed will have a double socket IP only for LED.

The power to the shed be fed from second connection box to double socket.

I have posted this to an electrical forum, but people are discussing different things and not my specific question.

This is why tried the IET forum, so competent people/engineers can give me advice. If the above-mentioned setup sounds good or not, please reply.

Thank you advance.

Parents
  • I also feel that SWA would be preferable it is cheap, easy to install and very suitable for uses such as this. RCD protection is required for outdoor sockets.

  • NYY-J us suitable for External fuxed installation and Direct Burial and is compliant with British standards. 

    BSEN/IEC 60332-3-24(c): Ensures fire performance standards 

    BS EN 60502-1: A standard that some NYY-J cables are manufactured to 

    BS7671: UK wiring regulations for burying cables in the ground 

    NYY-J cables are also compliant with other standards, including: VDE0295, IEC 60228, CENELEC HD383, and VDE0276. 

    NYY-J cables are PVC insulated and sheathed power cables that can be used for fixed installations in a variety of environments. They are resistant to moisture, UV exposure, and mechanical stress. NYY-J cables are suitable for indoor, outdoor, and underground use, but they should not be buried directly. When buried, they should be installed in a duct or conduit to protect them from mechanical damage.

  • When buried, they should be installed in a duct or conduit to protect them from mechanical damage.

    When buried they shall be installed in a duct or conduit that has equivalent mechanical protection [to a cable with overall earthed metallic armour or screen suitable to act as a protective conductor] ...

    See Regulation 522.8.10 of BS 7671.

Reply
  • When buried, they should be installed in a duct or conduit to protect them from mechanical damage.

    When buried they shall be installed in a duct or conduit that has equivalent mechanical protection [to a cable with overall earthed metallic armour or screen suitable to act as a protective conductor] ...

    See Regulation 522.8.10 of BS 7671.