Schockets and power to shed using 2.5mm NYY-J

I need some advice about running power to flower beds and a shed using 2.5mm NYY-J cable and whether it complies with BS.

The cable will feed from the consumer unit using a 16A MCB to an outside connection box to feed both sides of plants (as diagram provided).

The cable size and MCB were chosen based my needs and the limited power to be drawnThe cable will not be buried but will run along the perimeter of my fence on top of a 20mm pipe (not plastic conduit) secured either with plastic or metal cable ties.

The pipe will secured the concrete fence posts150mm above the ground heavy-duty saddles.

Each bed will have a double socket IP only for LED.

The power to the shed be fed from second connection box to double socket.

I have posted this to an electrical forum, but people are discussing different things and not my specific question.

This is why tried the IET forum, so competent people/engineers can give me advice. If the above-mentioned setup sounds good or not, please reply.

Thank you advance.

Parents
  • Personally, I wouldn’t be bothered with SWA if this was a job in my own house. NYY-J cable is easy to work and connect into plastic enclosures and is suitable for outside use. It is a robust cable and can be buried direct, albeit contrary to 7671 if without further appropriate mechanical protection.

    I have loads of it about my own garden. Shoved up a bit of 32mm waste pipe when I put it under the lawn.

    So does that comply? Well perhaps not with 522.8.10 of 7671, but it does with the same regulation in the Irish Standard. In the latter, the designer can make the determination on a suitable buried depth that would minimise the risk of mechanical damage. 

Reply
  • Personally, I wouldn’t be bothered with SWA if this was a job in my own house. NYY-J cable is easy to work and connect into plastic enclosures and is suitable for outside use. It is a robust cable and can be buried direct, albeit contrary to 7671 if without further appropriate mechanical protection.

    I have loads of it about my own garden. Shoved up a bit of 32mm waste pipe when I put it under the lawn.

    So does that comply? Well perhaps not with 522.8.10 of 7671, but it does with the same regulation in the Irish Standard. In the latter, the designer can make the determination on a suitable buried depth that would minimise the risk of mechanical damage. 

Children
  • the designer can make the determination on a suitable buried depth that would minimise the risk of mechanical damage

    To be honest, a suitable depth of burial is what's required with SWA and cable in ducts in any case ... the difference in BS 7671 being that, if buried, the cable has to be "armoured" (or equivalent), or buried in a duct that provides "equivalent protection".

    When you look at what depth an underground duct is required to be, this can be affected by pressure exerted on the surface of the ground ... this can lead to depths of burial far in excess of the "general purposes" guidance in GN1 of 500 mm, or the 600 mm required by BS 7671 for agricultural (non-cultivated) land.