Increasing csa through warm section of an installation

Consumer unit & gas ch combi to be installed in a brick cupboard (1200 x 1200 x 2500, with concrete ceiling ) just off the kitchen. The only cable route out is up over the door and through the brick wall to the main house. I've decided on perforated tray 225mm wide for good spacing which will be mounted 10mm from the wall. I'm comfortable with the cable selection for the 6 circuits on the tray and believe I can negate the grouping factor as per note 2 for table 4C1.

For example;  the kitchen ring final ; design current of 30a, will require 6mm T&E through the hot area ( I've called the ambient temp 45 degrees) but crucially I'd like to reduce this to 4mm once I'm in the room itself and terminating to the sockets Similarly I'd intend to install the lighting cicuits through the utility cupboard and 2 metres beyond to a common junction box at standard ambient where I would reduce to 1.5mm for distribution & terminations. Is this a viable startegy and/ or am I missing a regulations prohibition?

Thanks for any comments,

Pete Murphy

Parents
  • Hi Pete. Is the final circuit a ring final circuit? regulation 433.1.204 relates to each leg of the ring final circuit. In your calculations does each leg of the ring need to be 6.0mm to carry equal to or greater than 20 Amps ? 

  • there are usually better solutions than running low temperature cables thought hot zones or too tightly grouped, In your solution you will struggle to get two lots of 6mm into any normal fitting intended for 2.5mm. a cable with a higher temp rating, or routing lower down, or less grouped would all be things to consider first.

    Mike

  • Hello,

    As you'll see from my other replies the initial arithmetic was flawed and/ or incorrect correction factors. I've read 433.1.204 again.

    Thanks for your time,

    Pet