Hello,
We have a main MCCB panelboard on a client's site in a new building, that has the incoming cable from their nearby substation (not DNO) terminating into the switch disconnector within the MCCB panelboard.
There is no adjacent external/separate switch next to the panelboard.
To isolate the whole MCCB panelboard, the fuses need to be pulled from the nearby upstream substation, which belongs to the client, so organising such is not a big issue.
To isolate all the outgoing circuits from the panelboard and all the downstream MCB DBs that are within the building, the integral switch disconnector inside the panelboard will provide.
The proposed building maintainer has intimated that they think this contravenes 462.2.
They say that the busbars within the panelboard would fall under 462.2 that requires 'isolation for all live conductors'.
However our take on it is that the integral switch disconnector does isolate all the busbars and outgoing circuits inside/on the MCCB panelboard. Only the live side terminals on the switch disconnector will remain live.
Question is;
Is the above setup compliant with 462.2? Or, is a separate/adjacent main intake switch needed upstream of the MCCB panelboard to comply?
Thanks.