Regulation 551.7.2 - Generating Sets Operating in Parallel with Grid Fed Electrical Supplies (specifically solar PV related)

I know there have been a few discussions based on this but none I can’t find relating to a commercial three-phase roof mounted solar PV installation.

With regards to regulation 551.7.2, do you have to use the rated AC output current of inverter(s) for Ig(s), or can you take an engineered approach based on what can actually be generated at any one time?

InA ≥ In + Ig(s) where:

InA is the rated current of the assembly (consumer unit or distribution board for e.g.)

In is the rated current or current setting of the incoming circuit overcurrent protective device either incorporated within the low voltage switchgear and control gear assembly or upstream of it

Ig(s) is the rated output current of the generating set or sets.

 

If you had 2 inverters with a maximum rated AC output of 200A 3PH each as stated on manufacturer data sheet, you would say that Ig(s) is 400A 3PH total for an array with all PV modules facing in the same direction. 

However, if half of your PV array was facing East and was connected to one inverter, and the other half connected to the second inverter was facing West, you would never generate the maximum rated output at any one time, as it would be reduced to 200A approx. 

Therefore, could you use this lower figure of 200A for Ig(s) to satisfy this regulation or is it explicit that the combined maximum rating of 400A for all inverters should be used, even if it couldn’t be reached?

My concern is that LV assemblies may need to be rated to a higher current that in reality, would never be present due to the managed design of the PV system. 

Also, that existing installations whose LV assemblies were built before solar PV was widely used, could not benefit fully from an appropriately sized solar PV installation.

Thanks

P.S.

The above situation is based on the 2 inverters being cabled back to a dedicated 3PH MCCB sub LV panel board, which is then cabled back to a 3PH main LV switchboard at the intake.

I do realise one fix could be to set down the protective device upstream of the main LV switch board however it would take some convincing of the client to do so, even though I know their load profile would allow it! So please humour me and disregard that option.

Parents
  • With regards to regulation 551.7.2, do you have to use the rated AC output current of inverter(s) for Ig(s), or can you take an engineered approach based on what can actually be generated at any one time?

    Well, I don't understand this question.

    Because if the inverter has to be rated to output the total load of all panels, why not the connecting circuit, and the distribution board that the inverter connects through? What i mean by that, is that if Ig(s) is the AC output of the inverter, then surely you address that by the rating of the inverter (if it really can only output maximum what the panels can provide at any one time ... why would you put an over-rated inverter in?)

  • Hi and thanks for your response.

    The 2 inverters in my scenario are not over-rated, they each have half of the array connected to them which is sized to output the inverter maximum of 200A AC under ideal conditions. However, as half of the array faces East and the other West, in reality Ig(s) will never be 200+200=400A. One half will see up to 200A early in the day, and the other will see 200A later in the day. 

    Therefore, in reality, due to this East-West engineered approach, I would like to take Ig(s) to be a lower figure of say 250A (to be firmed up with PV simulation software).

    The way 551.7.2 is worded, to comply I believe I am required to take Ig(s) to be 400A.

    I agree with this in situations where all PV modules face the same way, however in my case of East-West, 400A will make In+Ig(s) greater than InA, which of course is non-compliant.

    So my question is, do you have to sum the AC output of all inverters together to determine Ig(s), or for an East-West situation can you apply engineered logic to arrive a lower, more accurate and no less safe figure?

    If this engineered approach was deemed acceptable, would it need to be documented by say a derogation from this particular regulation and / or a risk assessment? Thanks

Reply
  • Hi and thanks for your response.

    The 2 inverters in my scenario are not over-rated, they each have half of the array connected to them which is sized to output the inverter maximum of 200A AC under ideal conditions. However, as half of the array faces East and the other West, in reality Ig(s) will never be 200+200=400A. One half will see up to 200A early in the day, and the other will see 200A later in the day. 

    Therefore, in reality, due to this East-West engineered approach, I would like to take Ig(s) to be a lower figure of say 250A (to be firmed up with PV simulation software).

    The way 551.7.2 is worded, to comply I believe I am required to take Ig(s) to be 400A.

    I agree with this in situations where all PV modules face the same way, however in my case of East-West, 400A will make In+Ig(s) greater than InA, which of course is non-compliant.

    So my question is, do you have to sum the AC output of all inverters together to determine Ig(s), or for an East-West situation can you apply engineered logic to arrive a lower, more accurate and no less safe figure?

    If this engineered approach was deemed acceptable, would it need to be documented by say a derogation from this particular regulation and / or a risk assessment? Thanks

Children
  • I agree with this in situations where all PV modules face the same way, however in my case of East-West, 400A will make In+Ig(s) greater than InA, which of course is non-compliant.

    So my question is, do you have to sum the AC output of all inverters together to determine Ig(s), or for an East-West situation can you apply engineered logic to arrive a lower, more accurate and no less safe figure?

    If this engineered approach was deemed acceptable, would it need to be documented by say a derogation from this particular regulation and / or a risk assessment? Thanks

    To answer this, I would have to "interpret" BS 7671, which I'm not permitted to do ... in fact, only a court of law can do that.

    You could seek a professional opinion (or indeed hold your own), but if anything were to go awry, it would still be open to scrutiny in court?

    As such, I think all anyone could offer in response to this question at this stage, is that if, and only if, you (and if applicable your PI insurer) are happy to rely on the modelling providing a particular maximum of Ig(S), it seems like a reasonable approach. It all, I guess, rests on the reliability and caveats involved in the modelling ... would it stand up to external scrutiny ?

    I think that a better approach to improving on the validity of the assumption would be to include curtailment, so that if your modelled/calculated Ig(S), is exceeded, one of the inverters is curtailed accordingly? This would also align with one of the methods put forward in Section 9.3.4.2 of the IET Code of Practice for Electrical Energy Storage Systems, 3rd Edition, for meeting Regulation 551.7.2 of BS 7671?

  • Have you worked out what the generation will be around midday on a sunny June day?  The sun will be directly overhead, so illuminating both sets of panels.  Depending on the mounting angle of the panels, you could get something close to the kWp rating from both sets of panels at he same time.

  • Hi, this is a good point and yes it is has been considered. Thanks

  • around midday on a sunny June day?  The sun will be directly overhead,

    Not directly overhead - at least in the UK as we're far north of the Tropic of Cancer (which is only about 23 degrees N) - but I agree the sun could easily be high enough to illuminate both sets of panels simultaneously.

       - Andy.