Hello, Does anyone know if there are regulations stating that the 13A switch fuse spur can run Continuously at is rated current for long hours? I find this intriguing because, when a spur operates at its maximum rating, it tends to overheat, but i can't find any regulation that explicitly states this isn't allowed. The only regulation i can find in the 7671 concern installation cable size, etc. I know that electricians need to take cable size into account during installation but most of them just follow the standard, without considering the 80% rule from current capacity. the issue i have is that, although it's good practice, i can't find a regulation explicity stating this. So, i'm not sure what to rely on when it comes to the regulations. Does anyone have any insights?? 

Parents
  • My personal view is that fused connection units should not be used for a long hour load of more than about 10 amps, say 2.3 or 2.4 Kw. That is however my personal view of good practice and not a regulatory requirement.

    Equipment with a stated nominal loading of 10 amps could use up to 11 amps actual due to a combination of manufacturing tolerances and supply voltage fluctuations.

    I would have little concern with short term or intermittent loading to a full 13 amps nominal, and perhaps 14.2 amps actual.

    For long hour loads exceeding 10 amps, or short term loads exceeding 13 amps nominal, I would consider it best to avoid 13 amp fused connection units entirely, and instead use a dedicated radial circuit from a 16 amp or 20 amp MCB, and a local 20 amp switch if required. 

Reply
  • My personal view is that fused connection units should not be used for a long hour load of more than about 10 amps, say 2.3 or 2.4 Kw. That is however my personal view of good practice and not a regulatory requirement.

    Equipment with a stated nominal loading of 10 amps could use up to 11 amps actual due to a combination of manufacturing tolerances and supply voltage fluctuations.

    I would have little concern with short term or intermittent loading to a full 13 amps nominal, and perhaps 14.2 amps actual.

    For long hour loads exceeding 10 amps, or short term loads exceeding 13 amps nominal, I would consider it best to avoid 13 amp fused connection units entirely, and instead use a dedicated radial circuit from a 16 amp or 20 amp MCB, and a local 20 amp switch if required. 