13A Switch fuse spur

Hello, Does anyone know if there are regulations stating that the 13A switch fuse spur can run Continuously at is rated current for long hours? I find this intriguing because, when a spur operates at its maximum rating, it tends to overheat, but i can't find any regulation that explicitly states this isn't allowed. The only regulation i can find in the 7671 concern installation cable size, etc. I know that electricians need to take cable size into account during installation but most of them just follow the standard, without considering the 80% rule from current capacity. the issue i have is that, although it's good practice, i can't find a regulation explicity stating this. So, i'm not sure what to rely on when it comes to the regulations. Does anyone have any insights?? 

Parents
  • Hello everyone,

    Thank you for your messages. I did some further digging and came across Regulation 433.1.204 and Appendix 15 of BS 7671, which state that cables should have a minimum current-carrying capacity of 20A and should not be subjected to continuous loads exceeding this for extended periods.

    I believe this information is crucial when considering the use of switched fused spurs.

    Thank you all again for your feedback!

  • Regulation 433.1.204 and Appendix 15 of BS 7671, which state that cables should have a minimum current-carrying capacity of 20A and should not be subjected to continuous loads exceeding this for extended periods.

    I think that's referring to the rating of the cables making up the ring itself - where you have two 20A cables on a 32A protective device and is trying to ensure the loads are not so unevenly distributed around the ring that one of the legs can overheat even though the total load is within the rating of the protective device.

       - Andy.

  • Thank you for your messages. I did some further digging and came across Regulation 433.1.204 and Appendix 15 of BS 7671, which state that cables should have a minimum current-carrying capacity of 20A and should not be subjected to continuous loads exceeding this for extended periods.

    I agree, this is for ring final circuits only. The pertinent requirement to which I referred is Regulation 433.1:

Reply
  • Thank you for your messages. I did some further digging and came across Regulation 433.1.204 and Appendix 15 of BS 7671, which state that cables should have a minimum current-carrying capacity of 20A and should not be subjected to continuous loads exceeding this for extended periods.

    I agree, this is for ring final circuits only. The pertinent requirement to which I referred is Regulation 433.1: