4mm SWA - 2 circuits

Hi All, 

I have an install with a 4mm 5 core SWA buried that is setup as follows: 

L&N - circuit 1 (2x 13A sockets) - 16A MCB

L&N - circuit 2 (1x 16A socket outlet) - 16A MCB

CPC - for circuits 1 & 2

Maximum distance 30 metres. The client wants to upgrade the 16A socket to a 32A variant for a hot tub with a 32A MCB. 

Will this suffice and how will grouping factors affect this? The other circuit with 2x double sockets are used for lawnmowers and some lighting, and highly unlikely will have a sustained load.

I’m looking at grouping factors given that this is a multi core cable. Will the 4mm handle the increased load or would a 6mm be a better option? There is also capacity for reduction given the socket circuit would likely be loaded a lot less than its overall rating (the 30% grouping factor rule).

The cable is buried and running a new cable would be difficult so would prefer to use the existing 4mm. 

Thanks. 

Parents
  • Under the conditions of use expected, with minimum load on the 13 amp sockets I suspect that this proposed installation will be fine, it is the sort of thing that I might do for myself of for friends/family.

    I would be reluctant however to do this for a paying customer, as patterns of use might change. Nothing prevents the 13 amp sockets being loaded to 16 amps forever or to 20 amps for some hours.

    A better solution IMHO would be to double up the cores, so as to give 8mm for phase and for neutral, protect by a 40 amp or 45 amp MCB at the supply end. At the load end, fit a 2 way consumer unit with a 16 amp MCB for the 13 amp sockets and a 32 amp MCB for the 32 amp socket.

    Either final circuit may then be fully loaded without concerns, though not both at the same time. The two MCBs in series will probably not discriminate in the event of a short circuit, but that is arguably a price worth paying.

  • I am starting to see this as a realistic approach. It is for a friendly customer so should be fine. The socket circuit will be limited to 16A, which would be below the reduced grouping factor loading. 

Reply
  • I am starting to see this as a realistic approach. It is for a friendly customer so should be fine. The socket circuit will be limited to 16A, which would be below the reduced grouping factor loading. 